Just wondering if I got this right but is it ok to take a 2.5mm spur from a 32MCB ring main Or should I use 4mm cable.
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss Spur from 32MCB in the UK Electrical Forum area at ElectriciansForums.net
This is a common misconception, 'multiple circuits' in one MCB is an impossibility by definition. If there is one point of connection to a protective device at the source of supply it is one circuit no matter how many cables are connected.I see plenty of EICRs stating that 'multiple circuits' are connected into 1 breaker and need rectifying. On inspection it's often just a spur taken from ring at MCB and no issue at all!
Suprised no one has asked what your design current will be ???Just wondering if I got this right but is it ok to take a 2.5mm spur from a 32MCB ring main Or should I use 4mm cable.
Reply to Spur from 32MCB in the UK Electrical Forum area at ElectriciansForums.net