Hi chaps...
Been asked to add a light in an under-stairs cupboard.
A spur from the downstairs socket circuit runs through that cupboard to a double 13A outlet in the kitchen. I'd like to tap into that for the light, but under the regs I'd have to fuse it down first.
The thing is, the 2.5mm T+E used is rated for 27A (in this case, method C). Worse case scenario is that both those sockets are used at 13A, so that's 26A being drawn.
The light which is going to be fitted is a very low energy LED fitting, so uses next to nothing. If the light is on and the sockets are used, the maximum that could be drawn through the spur is only ever so slightly over 26A, so the cable is still not overloaded.
Would anyone NOT fuse the spur in this instance (as it's clearly not a risk), or should it be done anyway as per the regs (and have the inconvenience of the blown 13A fuse if the toaster and kettle are used together)
Been asked to add a light in an under-stairs cupboard.
A spur from the downstairs socket circuit runs through that cupboard to a double 13A outlet in the kitchen. I'd like to tap into that for the light, but under the regs I'd have to fuse it down first.
The thing is, the 2.5mm T+E used is rated for 27A (in this case, method C). Worse case scenario is that both those sockets are used at 13A, so that's 26A being drawn.
The light which is going to be fitted is a very low energy LED fitting, so uses next to nothing. If the light is on and the sockets are used, the maximum that could be drawn through the spur is only ever so slightly over 26A, so the cable is still not overloaded.
Would anyone NOT fuse the spur in this instance (as it's clearly not a risk), or should it be done anyway as per the regs (and have the inconvenience of the blown 13A fuse if the toaster and kettle are used together)