Apologies if this has already been posted but I can’t find the answer.

It is considered ok to be able to install a socket outlet spurred from a 32A ring. Would it be considered ok to install one single socket directly from the 32A MCB in 2.5 T&E.

One socket straight from the MCB would become a radial, however I can’t understand the difference between installing a socket from MCB and taking a spur from another socket.

Hope this makes sense, cheers
 
either way, your socket would be classed as a spur. you can fit 1 single or 1 double socket on an unfused spur, either from a socket or from the MCB (RCD protection must be present).
 
Ya they're both considered spurs

I suppose you could consider the double socket a fixed load in a way as i think they're rated at 20A so probably risk of overcurrent not that great

We've outlawed the unfused spurs here(domestic anyway afaik)
So you've got to fuse at 13amp when spurring off a rfc
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Grimsby
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Electrical Engineer (Qualified)

Thread Information

Title
Spur from ring
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
3
Unsolved
--

Advert

Thread statistics

Created
brodders97,
Last reply from
Mikegh,
Replies
3
Views
1,807

Advert

Back
Top