Hi, we’ve fitted a breakfast bar in the kitchen. There was a disused socket above it which we are going to extend to a single socket, then spur off that to a 3A FCU. Would this be classed as spurring off an existing spur?

The old 2 gang socket will be replaced by a junction block or 20amp switch, so in theory we would only be extending the socket.

Would this be safe or are there any other options to this?

Cheers

[ElectriciansForums.net] Spur off a spur to 2W LED
 
If you are replacing the twin socket with a "junction box" but leaving only one leg to the single socket it's still a spur as it's not on the ring. So it would still be a spur off a spur. If you extend the 2 legs of the double socket to the single socket this would keep the ring. Then the spur off for your light.
 
I would change the twin socket for a switched fused spur then everything is protected. Probably some stupid reg that says you can't!
Trouble is, most of the regs concerning spurring off the ring go back 40 years when people didn't have gas central heating and they were afraid that a 2 or 3 KW fire would be plugged into spurred off sockets, it just doesn't happen in this day and age.
Wait for it.......The reg's police will be saying ah but what if?
Am I bovered!:)
 
Hi, we’ve fitted a breakfast bar in the kitchen. There was a disused socket above it which we are going to extend to a single socket,[/QUOTE]
If you are going to extend to the single socket why not put all on the ring?
 
Hi, we’ve fitted a breakfast bar in the kitchen. There was a disused socket above it which we are going to extend to a single socket,
If you are going to extend to the single socket why not put all on the ring?[/QUOTE]

Hi, i’ve already run a single 2.5 cable from the disused socket to the new location which has been channeled in wall and plastered over now.
 
This is one of those paradoxical situations where the compliant method - fuse the whole spur, then you can do what you like - is actually less sensible and a poorer engineering solution than the non-compliant one.

The principle of not having more than one point on a spur is to prevent the cable being overloaded and avoid a heavy point load on the ring. But here, the offending 'second' outlet is a 2W lamp, which has absolutely negligible consumption and can be ignored for loading purposes. The only reason it might cause a problem is if, in the future, someone replaces the light and/or its FCU with a heavy load, without first checking how it is wired.

Personally, I would rather not pass the socket current through an FCU and its 13A fuse just to make the circuit comply, but technically, that is what is required. It does have the advantage that multiple sockets can be fitted if desired for low load appliances, even though there is only one at the moment.
 

Reply to Spur off a spur to 2W LED in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
450
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Yes… as long as the initial radial circuit is designed properly regarding OCPD, cable size and rcd protection.
Replies
1
Views
838
  • Question
One thing you may find is that it will most probably be a 6mm cable and to get two of them in to a terminal may prove to be a stumbling block if...
Replies
3
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top