32A breaker, labelled kitchen socket ring, 3 wires coming out of it. All look like 2.5mm2, two of them are same shade of brown so I suspect they will be the ring, and another to an unlabeled T&E. I know some cowboys did the kitchen, they did get involved with the electrics. I suspect this will go to an extra socket that was wanted nearby, haven't checked yet.
It looks wrong, personally I would have just put it on its own 20a breaker. But when I thought about it, how different is this setup to spuring off the ring elsewhere? You are still going to junction 3 cables together at some point, what is the extra risk of doing it at the breaker? It will make ring testing slightly more awkward, but otherwise?
32A breaker, labelled kitchen socket ring, 3 wires coming out of it. All look like 2.5mm2, two of them are same shade of brown so I suspect they will be the ring, and another to an unlabeled T&E. I know some cowboys did the kitchen, they did get involved with the electrics. I suspect this will go to an extra socket that was wanted nearby, haven't checked yet.
It looks wrong, personally I would have just put it on its own 20a breaker. But when I thought about it, how different is this setup to spuring off the ring elsewhere? You are still going to junction 3 cables together at some point, what is the extra risk of doing it at the breaker? It will make ring testing slightly more awkward, but otherwise?