Is spurring off a sockets that’s already been spurred off a major no no?? It’s for a socket behind a wall mounted tv so not gony be a major load on the cable
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss Spurring of a spurred socket in the UK Electrical Forum area at ElectriciansForums.net
The wiring regulations are not statutory, and departures are permitted where it can be demonstrated that the resulting degree of safety is not less than that obtained by compliance.
Nobody can give a valid reason why a single socket spurred from another single socket itself wired from a spur is any less safe than a double outlet on a spur. There is no more chance of overloading the supply cable, or the outlets themselves, and it can be tested and verified in the same way as any other wiring.
Departures are permitted but there’s a difference between a departure and a non compliance
Because a spur constitutes a single or a double outlet"I think if someone supplied a certificate for such work, noting the departure and attaching a risk assessment (even a simple one), then I wouldn't immediately consider it bad practise.
However, I wonder if there is more risk of maximum load being run on two single sockets, perhaps with multi gang extensions in each if they are the only sockets in the room - at which point you could run 14A through each without a fuse tripping. (Though these days there are fewer things outside of heating that get close to that of course)"
Are you suggesting that an end user would think there is a difference between what he can plug into a single socket and a double socket?
It does not matter how many muti-gang extensions are run off a 13a outlet, they are protected against overload by a 13a fuse in the plug.
"Double socket designers clearly have decided that the risk of both outlets being run at maximum is low enough to justify their rating. In the case of single sockets the installer is becoming the designer and has to justify that risk."
Again, an end user will not differentiate between a single or double outlet, he sees a 13a socket and plugs whatever he wants into it
"If I were assessing the situation for continued use in an EICR I think I'd be working from the starting point of a C2 and looking whether there are reasons it should not be noted as such."
I disagree. I cannot see how a double outlet on a spur is safe and compliant but two single outlets are potentially dangerous. Illogical.
"If it was in a bedroom with no heating and a heater or hairdryer might be plugged in I might judge it differently than if it was behind a TV as in this case and less likely to be used for anything else."
"However, what would happen when the next owner comes along and decides to get that single socket replaced with a double by her handyman who isn't as careful as the original installer? Should the original installer be taking that possibility into account? I honestly don't know the answer to that... Would a judge consider him to have no responsibility if something were to occur?"
What if the handyman extends the ring in 1.0mm, what if he changes the OCPD for a 50a?
Those working with electrics in dwellings are required to be competent. We cannot be responsible for what happens to an installation after we have handed it over.
"The answer to the original question is clearly no it's not compliant. However it may well be safe in most circumstances, but possibly not all".
In which would it not be safe?
My answers in red
Only to those who behave like lemmings and are unable to actually apply some logic to whatever they are doing.Because a spur constitutes a single or a double outlet
These are the same people who made 13a RCD protected socket outlets non compliant for additional protection in Bs7671 2018.Before any other scouser chirps in, I will quote one of their favourite phrases....
"Eeeh... calm down, calm down!"
No point trying to argue the case... BS7671 says its non compliant, therefore we shouldn't be doing it, or advising that its safe to do so.
Non compliant, if this is indeed an RFC, wired in 2.5, off a 32A OCPD.
The ideal solution has been suggested, early on.. (13A FCU supplying the spur) Arguing over why it 'could' be done, or speculating why it shouldn't just in case an idiot comes along later...
These conversations have no doubt been discussed before any regs were published, and they've come up with "only one unfused spur from an RFC"
Does it though? I know it's not permitted according to the design guide in app. 15, but which regulation does it break? (still talking about the singles scenario)BS7671 says its non compliant
Because bs 7288 says they are not suitable for additional protection hence why they were removed.These are the same people who made 13a RCD protected socket outlets non compliant for additional protection in Bs7671 2018.
"I think if someone supplied a certificate for such work, noting the departure and attaching a risk assessment (even a simple one), then I wouldn't immediately consider it bad practise.
However, I wonder if there is more risk of maximum load being run on two single sockets, perhaps with multi gang extensions in each if they are the only sockets in the room - at which point you could run 14A through each without a fuse tripping. (Though these days there are fewer things outside of heating that get close to that of course)"
Are you suggesting that an end user would think there is a difference between what he can plug into a single socket and a double socket?
It does not matter how many muti-gang extensions are run off a 13a outlet, they are protected against overload by a 13a fuse in the plug.
"Double socket designers clearly have decided that the risk of both outlets being run at maximum is low enough to justify their rating. In the case of single sockets the installer is becoming the designer and has to justify that risk."
Again, an end user will not differentiate between a single or double outlet, he sees a 13a socket and plugs whatever he wants into it
"If I were assessing the situation for continued use in an EICR I think I'd be working from the starting point of a C2 and looking whether there are reasons it should not be noted as such."
I disagree. I cannot see how a double outlet on a spur is safe and compliant but two single outlets are potentially dangerous. Illogical.
"If it was in a bedroom with no heating and a heater or hairdryer might be plugged in I might judge it differently than if it was behind a TV as in this case and less likely to be used for anything else."
"However, what would happen when the next owner comes along and decides to get that single socket replaced with a double by her handyman who isn't as careful as the original installer? Should the original installer be taking that possibility into account? I honestly don't know the answer to that... Would a judge consider him to have no responsibility if something were to occur?"
What if the handyman extends the ring in 1.0mm, what if he changes the OCPD for a 50a?
Those working with electrics in dwellings are required to be competent. We cannot be responsible for what happens to an installation after we have handed it over.
"The answer to the original question is clearly no it's not compliant. However it may well be safe in most circumstances, but possibly not all".
In which would it not be safe?
My answers in red
While not technically compliant I can see no real problem with spurring a single socket from another single socket which itself is a spur.
I beg your pardon? I'm not into the IET Gestapo.Well you should be.
Probably because it is quite common for DIY changes from a single socket to a double. Then you end up with 4 * 13A outlet points on the spur.I don't know why it was changed but can only assume it was done for a reason.
Reply to Spurring of a spurred socket in the UK Electrical Forum area at ElectriciansForums.net