I'm looking at running 25mm SWA to supply secondary CU to future proof HMO design. See my previous threads for details House of Multiple Occupancy Design - https://www.electriciansforums.co.uk/threads/house-of-multiple-occupancy-design.124817/

My issue is a 100A CU and SP Distribution boards seem to only have 16mm neutral terminals from what I can find. So I'm stuck, can you buy bigger terminals, if not what about placing Henley block in CU/SP Distribution board to run main neutrals. At the risk of being scalded, dare I say drill out to accommodate 25mm ?
Otherwise only solution would be to buy 3Phase which seems like massive overkill for what I'm looking to do.
 
Looking at the other thread, it's an HMO with 12 rooms that might be separately let. If the communal GCH packs in. 12 x 2kW fanheaters will go on. There are also some electric hobs.

Returning to the subject of terminating 16 & 25mm² in DB's, we sometimes have to do this where the cable has been selected for VD or running through very high ambient temp. A terminal pin is OK, it won't automatically reduce the CCC, but then typically you won't hit the CCC with the kind of outgoing way you will have in a regular 60898 DB. Beware the effect of poor quality terminals though, sometimes they don't hold well on a solid lump of copper. Tthe same is true of solid MI cores which can be a problem to terminate in marginal single-screw terminals.

An alternative is to use an inline uninsulated butt crimp sized for the SWA core, with a tail of smaller cable with the correct number of strands carefully doubled over inwards, so that all strands contact the crimp. A suitable length tail will allow flexibility to minimise stress on the terminal.

I have been known, when pressed, to put three strands in one hole and four in the next, but I don't recommend it. I would be more likely to do this on an outsize EC, where it also gives the advantage of redundancy.

FWIW here's a pic of a 60898 board with 3x 3-phase 50A outgoing circuits in 16mm², admittedly conduit cable. I didn't wire the straggly stuff in the background, only the 16mm.
View attachment 39943
Hmmm, MCBs are upside down, copper showing at the terminations, confusing conductor identification.
Codes C2, C2 & C3.
 

Reply to Square peg round hole....... in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
300
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
812
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
864

Similar threads

  • Question
And exciting when that Hager AFDD finally tripped 😂
2
Replies
28
Views
2K
nicebutdim
N
  • Question
Nothing wrong with it. Which manufacturers have you got this information from? What do you mean by trip speed? Fuses and MCBs can operate in the...
Replies
11
Views
2K
davesparks
D

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top