4 pole manual change over switch is present with type 2 spd conncetion and then 3 phase and a neutral of length(35m) is then connected to volatge stabilizer,stabilizer output is connected to standby generator ( generator has contactors which are not damage so far ) then its output is then connected to online UPS (three phase in and single phase out )As I said I have been thinking on your problem so more questions for you.
Do you have a transfer switch to connect the installation between utility supply and generator supply? Is it manual or automatic?
What are the approximate lengths of cables - perhaps you could provide a one-line layout drawing which shows the electrical items and the cabling between them. This is relevant because for a short interconnection one surge suppressor could be effective but for a longer length - which can pick up lightning pulses like an antenna - a surge suppressor at each end of the interconnection is probably required.
Similarly all the earth/ground/bonding need to be short and have a high surface area - a low surge impedance; otherwise they present a high impedance to short high intensity lightning pulses which means they are less effective at conducting short-lived high currents to ground and thereby reducing overvoltages occurring at places in the installation where there are sensitive electrical components.
Does the building itself have lightning protection installed?
Volatge stabiliser and ups are grounded too
But problem is that only generator control panel and stabiliser display panel get damage which do not pass the line ,generator do not self start) and during normal lightning ,main utility line is cut off from manual change over and generator is operated under lightning condition ) and normal lightning ,generator was operating smoothly for three days lightning .after heavy lightning which was high enough to shake earth structure ( as per source ) ,control panel was badly burnt .(generator works perfectly great after controller replacement)
If possible , will you please send me your email id ?
[automerge]1584597466[/automerge]
4 pole manual change over switch is present with type 2 spd conncetion and then 3 phase and a neutral of length(35m) is then connected to volatge stabilizer,stabilizer output is connected to standby generator ( generator has contactors which are not damage so far ) then its output is then connected to online UPS (three phase in and single phase out )As I said I have been thinking on your problem so more questions for you.
Do you have a transfer switch to connect the installation between utility supply and generator supply? Is it manual or automatic?
What are the approximate lengths of cables - perhaps you could provide a one-line layout drawing which shows the electrical items and the cabling between them. This is relevant because for a short interconnection one surge suppressor could be effective but for a longer length - which can pick up lightning pulses like an antenna - a surge suppressor at each end of the interconnection is probably required.
Similarly all the earth/ground/bonding need to be short and have a high surface area - a low surge impedance; otherwise they present a high impedance to short high intensity lightning pulses which means they are less effective at conducting short-lived high currents to ground and thereby reducing overvoltages occurring at places in the installation where there are sensitive electrical components.
Does the building itself have lightning protection installed?
Volatge stabiliser and ups are grounded too
But problem is that only generator control panel and stabiliser display panel get damage which do not pass the line ,generator do not self start) and during normal lightning ,main utility line is cut off from manual change over and generator is operated under lightning condition ) and normal lightning ,generator was operating smoothly for three days lightning .after heavy lightning which was high enough to shake earth structure ( as per source ) ,control panel was badly burnt .(generator works perfectly great after controller replacement)
If possible , will you please send me your email id ?
[automerge]1584597468[/automerge]
4 pole manual change over switch is present with type 2 spd conncetion and then 3 phase and a neutral of length(35m) is then connected to volatge stabilizer,stabilizer output is connected to standby generator ( generator has contactors which are not damage so far ) then its output is then connected to online UPS (three phase in and single phase out )As I said I have been thinking on your problem so more questions for you.
Do you have a transfer switch to connect the installation between utility supply and generator supply? Is it manual or automatic?
What are the approximate lengths of cables - perhaps you could provide a one-line layout drawing which shows the electrical items and the cabling between them. This is relevant because for a short interconnection one surge suppressor could be effective but for a longer length - which can pick up lightning pulses like an antenna - a surge suppressor at each end of the interconnection is probably required.
Similarly all the earth/ground/bonding need to be short and have a high surface area - a low surge impedance; otherwise they present a high impedance to short high intensity lightning pulses which means they are less effective at conducting short-lived high currents to ground and thereby reducing overvoltages occurring at places in the installation where there are sensitive electrical components.
Does the building itself have lightning protection installed?
Volatge stabiliser and ups are grounded too
But problem is that only generator control panel and stabiliser display panel get damage which do not pass the line ,generator do not self start) and during normal lightning ,main utility line is cut off from manual change over and generator is operated under lightning condition ) and normal lightning ,generator was operating smoothly for three days lightning .after heavy lightning which was high enough to shake earth structure ( as per source ) ,control panel was badly burnt .(generator works perfectly great after controller replacement)
If possible , will you please send me your email id ?