Star Delta motor problem. | on ElectriciansForums

Discuss Star Delta motor problem. in the UK Electrical Forum area at ElectriciansForums.net

Joined
Feb 26, 2008
Messages
90
Reaction score
7
Location
Dublin,Ireland
So I have a 55kw Star Delta starting motor. The motor was moved about 10feet from original position so I had to put new cabling in from Isolator to Motor. That's all was changed.
When I went to start it it blew a fuse when kicking into Delta.
Changed fuse and it happened again only this time it was a different phase fuse blew.
Have checked operation of star Delta contactors with no load and they are working. Have also done an insualtion resistance test on motor windings and new cables and all ok.
Is it possible when it's going into Delta that it's also going into reverse?
Anyone any ideas of what else it could be?
 
So I have a 55kw Star Delta starting motor. The motor was moved about 10feet from original position so I had to put new cabling in from Isolator to Motor. That's all was changed.
When I went to start it it blew a fuse when kicking into Delta.
Changed fuse and it happened again only this time it was a different phase fuse blew.
Have checked operation of star Delta contactors with no load and they are working. Have also done an insualtion resistance test on motor windings and new cables and all ok.
Is it possible when it's going into Delta that it's also going into reverse?
Anyone any ideas of what else it could be?
Could be you have reconnected the Motor incorrectly, can you post a picture or a drawing of how you have connected the Motor? And the Starter.
 
Last edited:
You're shorting a phase through one of the winding's.

So when it changes to delta the motor is running on 2 phases.

Trace it out.

Edit

So for example L1 - U1 - U2 - L1 rather than L1 - U1 - U2 - L2

U1 and U2 being the start and end of a winding. L1 & L2 being phases.
 
You're shorting a phase through one of the winding's.

So when it changes to delta the motor is running on 2 phases.

Trace it out.

Edit

So for example L1 - U1 - U2 - L1 rather than L1 - U1 - U2 - L2

U1 and U2 being the start and end of a winding. L1 & L2 being phases.
Would that not show up on a Insualtion resistance test?
 
It sounds like you now have the same phase on the end of all three sets of windings, i.e L1 is across u1 & u2, L2 is across v1 & v2 and L3 is across W1 & W2.
As stated by Rob, starting at the starter, draw out the wiring all the way thru to the motor, then if you cannot spot what is worng post your sketch.
 
Glad you've got it sorted. The amount of trainees I've had make the same mistake first time I let them loose on one.

Don't get much call for star delta starters anymore with soft starts an vsds becoming cheaper.
 
Usually,someone decides to manually operate one of the contactors,whilst the other is energised,to "see if it changes the outcome" .....eye protection,obligatory :(
 

Reply to Star Delta motor problem. in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
438
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Hello, Last year my 30 year old Static Pase convertor stopped working, the 3 phase motor is 0.55KW / 0.74HP and drives a small lathe. When I...
Replies
0
Views
216
  • Question
Its important to remember that a plug top fuse is just a rewireable fuse that's convenient to change and shouldn't be confused with a HRC fuse...
2
Replies
15
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top