Static/Tingle from shower/towel rad. | Page 2 | on ElectriciansForums

Discuss Static/Tingle from shower/towel rad. in the UK Electrical Forum area at ElectriciansForums.net

Dunc88

-
Joined
Mar 22, 2017
Messages
29
Reaction score
4
Location
West Midlands
Hi, working in a property a couple of years old. Earthing System is a TN-C-S.
Customer’s daughter/wife have both complained about receiving a “slight tingle/static sensation” when using the shower in only one of the bathrooms (when touching the shower/or towel rad). I’ve checked the incoming water main & its plastic, so there’s no 10mm water bond. All circuits are protected by 30mA rcbo’s, nothing has tripped to date. Ive only taken a quick look (an hour on the way home yesterday) so running the shower (fed directly from boiler) & turning the rads on whilst checking it with my volt stick is as far as i’ve got, didnt feel anything myself but want to go back again today to have another look. Any advice appreciated.
 
I've fault-found a problem many years ago where there was tingling in a shower. After numerous visits and probably around 14 site hours investigating it turned out to be the drain which was broken under ground outside and a leaking garden light connection box next to it. When the outside lights switched on every evening the drain on the floor of the shower itself was elevating in voltage sufficiently to give someone a nasty tingle when they touched the taps.
Thats crazy isnt it! Makes you doubt yourself when u cant find something but when theres so many potential outcomes its always going to be tough I spose! Thanks for the reply!
 

Reply to Static/Tingle from shower/towel rad. in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
325
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
852
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
973

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top