A client has recently had a 10ft x 6ft Steel Cabin delivered. It will be a permanent addition for a block of flats outside for storing things in for contractors. They want a light inside and a floodlight outside.
Currently next to it about 5 yards away is a bin store which has a light in it from the main building which is on a 6A supply. The earthing System is PME. I can’t run a dedicated supply from the main building due to the amount of paths and obstacles now in the way.
Not keen to continue the PME into the steel container as it’s permanent, I’d rather TT. I have thought about coming from the Bin store supply into a 3A FCU, TTing the outgoing supply here and going into the cabin with this. Any thoughts?
 
Completing the job tomorrow. Nice and easy.
just a quick one, the steel container isn’t extraneous, I’ve only used class 2 light fittings inside. Does the steel container need a fly lead from the fused spur or would you just leave it?
 
I’m not sure that RCD spurs are compliant as they are not included in bs7671 and bs 7288 state that they only provide supplementary protection and that additional protection is assumed upstream.
 
How can a steel box forming the enclosure of the spur be an extraneous conductive part by definition,when it forms part of the electrical installation? Is it not an exposed conductive part rather than an extraneous conductive part ?
 
Of course it is extraneous ?. I’ll take a bond from the earths at the spur to the steel itself then ☺.
How can a steel box forming the enclosure of the spur be an extraneous conductive part by definition,when it forms part of the electrical installation? Is it not an exposed conductive part rather than an extraneous conductive part ?
wrong... by that you would have to say that any room with electrical equipment fixed to the walls, is a part of the installation.
 
Of course it’s part of the electrical installation, it forms the enclosure of the spur and is exposed ie class 1 an exposed conductive part.
afraid we have to disagree on this one. anyway Zebedee says "time for bed", :p :p
 

Reply to Steel Container in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
401
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
988
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top