Right, so its been one of those long days.

swift breakdown:
top floor flat.
lighting cable is single cores in a conduit system.

was employed to install downlights in 2 rooms.

Really bizarre one for me, ive never encontered nything like this before.

So i tested the original fittings in these rooms to establish an earth path, all was well.
1.16 zs.

wired all my downlights and then crimped onto the switc and neutral at the original fitting.
zs was 1776.

disconected my wiring, still 1776 ohms.

this was the same for both rooms.

ran a new earth from the MET (10mm)
the done a zs with that new earth and across the switch/neutral at the light.
still getting 1776.

Really confused as the ze on the property is really low (0.25ohms)

this problem is only happening on this lighting circuit.

Any ideas on this?

i had plan to wrap up for the big quarantine but ill need to go back out tomorrow
 
Put up some pics please. I've never seen a 30306 CU with integral RCD protection. I'd like to learn...
They are rare but there was a wylex standard range CU with RCD protection.

[ElectriciansForums.net] strange earthing problem (lighting)
 
Last edited by a moderator:

Reply to strange earthing problem (lighting) in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
291
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
800
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
830

Similar threads

Problems can arise when you get on too well then they think he won’t mind me doing a bit.
    • Friendly
    • Like
Replies
8
Views
440
  • Question
My bafflement increases. I swapped the offending light with one elsewhere on the back of the house - one of those that's on a circuit of its own...
Replies
5
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top