hi there, first post.

I’m having a very strange problem affecting my entire board.

I’ve just qualified but not that experienced in faults.

My home electrics have been having problems lately, every time we use the kettle/ toaster/ hairdryer, the lights dim. If we have the toaster on and use the kettle the toast pops up. The shower is juddering when turned on. And the washing machine doesn’t spin if there is a load in it. The microwave also sounds like it has less oomph when lights are on or other appliances being used.

It’s almost like there isn’t enough power to the circuits however I’ve tested for voltage on the outgoing side of all breakers/ Rcd’s and I’m well within the +/-10% supply.

My boss said it could be a neutral fault, I tightened all the neutrals up and all other connections for that matter. I also tried a new 100a main switch incase there was high resistance going on inside this. Still problems, it’s not like it’s just part of the board having problems because I’ve tried all combinations of circuits being on and off and also tried appliances on upstairs and downstairs circuits all of them seem to be problematic. There is no tripping, just feel s like nothing is getting enough juice to run how it should.


Any ideas?
Thanks
 
Tenner says it's a bad neutral connection in the tee off joint under the pavement.
I don't think there's any evidence it's a CNE fault, I would expect it to be the line connection that is high-resistance. The EFLI will be bad, the voltage will vary, but there won't be any other symptoms like tingles off things.

But what was overlooked early on, is that any bad connection with enough resistance to affect things this badly, when loaded with heating appliances, will get pretty hot itself. If nothing upstream of the DB busbars was evidently toasty, then there would have been little doubt that that it was the DNO's problem even before getting the voltmeter out.
 
I can see your point there Lucien - there would be tingles felt if the neutral had a high resistance joint. Although if all accessories are plastic then this may be masked.
 
Or, of course, that the equipotential zone is very effective and everything in the house is riding nicely on the faulty CNE. IIRC there was a thread on here with an open MEN in the street, where the only symptom was steam from the soil around a metallic water service that was shouldering the load of a few properties.
 
I've seen two failed neutral connections in tee joints under pavements. One was feeding my own property, and both were installed in the 1970s. DNO came out quickly to sort mine - piggy backed from next door neighbour''s meter cupboard with a temporary bit of concentric until the joint was fixed.
 

Reply to Strange fault, can’t work it out in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
413
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
Thanks. I do a lot more for the site than just change a few alarm batterys. EICRs, PAT, numerous little jobs. Never away from the place.
2
Replies
19
Views
2K
Seen this where T&E has been fixed with a flat bend of too tight a radius.
2 3
Replies
35
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top