Installed some new floodlights/pir and switches today. All tested fine, however on power up it was evident I had got something wrong. Upon investigation I had the neutral in the switched live of the PIR. Kicked myself but mistakes happen.

Corrected the mistake but still nothing was working as it should. Spent over an hour chasing the fault. Got to the metal clad RCD spur I had installed, live - cpc =245v, live - neutral = 110v, neutral - earth = 38v.

I got to the point of just having a piece of flex on the load side of the RCD and still getting the same results. Measurements are fine if you disconnect the cable. Fair to say I was stretching my head. Disconnected the RCD F/spur and tested the circuit again. All comes back ok. Wired all the lights up (bypassing all sensors/switches) and all works ok.

Has anyone come across a RCD behaving like this? Could my initial neutral/live fault have broken it? If so, how come a simple piece of flex causes these readings but no flex doesnt?
 
Best guess is that you have blown the neutral conductor somewhere.

Could be the N connection through the rcd. A volt measurement between live in and live out, followed by N in and N out will help track it down.
With a load attached, you should measure 0v from in to out on either the L or N
Any voltage showing, means a damaged unit.
 
You might have been lucky here. If the RCD is open-circuit in the neutral as it seems, it might have saved you from blowing up the PIR with the crossed connections.
 
Yep, neutral is open circuit.

Could I link out the neutral supply and load? As long as the rcd tests ok on the load side?
RCD measures the current in both L & N to detect anything missing. Bypass N and it would trip immediately I'm afraid as all L current would be seen as "missing" since it is not seen to come back via the local N.
 
Well, I'm a little overwhelmed here. Been over today to change rcd, test and commission the lights.

Getting some strange problems and I dont know if I'm missing the obvious. I cant think straight now. So here's the story.

As said earlier, I had a neutral on the switch return of 1 of the PIR sensors yesterday. Fault rectified but rcd was not working right. Not sure if it worked correct before the fault or now.

Today, upon a few hours of head scratching I found that the 3 way switch was not actually switching the load of the switch return from the PIRs. I tried a regular 1 way switch on the PIR switch and the motion sensors switched the lights as they should. Put the 3 way back on and the pir switch return was showing in terminal 1 but not actually passing it through to common. What are the chances. Left the 1 way switch on and all lights and sensors worked as they should.

After that, I decided to put an rcd spur back on the circuit. Circuit tripped immediately. The rcd just wouldn't hold in. The rcd was showing 115v on the load side even though the rcd would not hold in...

I disconnected the rcd and testing the circuit again. Maximum Zs I got on the circuit was 0.55ohms. Insulation resistance line and neutral to earth >200Mohms. Voltage on the circuit 254v between line and neutral, line and earth and nothing between earth and neutral. Put the lights back on the circuit and did a milliamps clamp reading on the earth. 0.08mA when lights not on, 0.69mA when all lights on. 0.48A on both neutral and line.

I'm really stuck here. I feel like I missing the obvious but because iv been mulling over it so much I cant think straight.

Any ideas?
 
When you say three way switch do you mean a 3gang switch mate or are you talking about a 2 way with auto/manual override positions ? Can you do a little drawing of your setup ?
A 3 position switch. L1, l2 and common.
 

Attachments

  • [ElectriciansForums.net] Strange fault
    16061947882186123987060976368504.jpg
    38.5 KB · Views: 35

Reply to Strange fault in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
380
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
957
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
I would add though that a typical good TT rod of 100 ohms only needs 3V to have 30mA flowing and so trip an RCD, you might find that sort of N-E...
Replies
8
Views
693
  • Question
I misread it.
    • Like
Replies
13
Views
942

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top