I've installed a garage consumer unit sub-main to an outbuilding in 16mm 3 core armoured, the insulation tests all come back fine - +800Mohms on a 500 volt test but when I power up the installation I get 90 volts leaking to Earth from Neutral and i'm not sure why. The Garage RCD also doesn't trip on the test button.

The circuit goes from a 32A mcb protected by RCD in the House Consumer Unit, in 10mm t&e to a 63A Rotary Isolator inside the house, then from the Rotary Isolator to the Garage Consumer Unit in 16mm Armoured run underground in Copex ducting.

The voltages at the Rotary Isolator are fine - 230V between L-N and L-E and 0V Between N-E.

Once the circuit is live, there's a 90 volt Leak to Earth from the Neutral, somewhere starting at the Rotary Isolator up to the Garage Consumer Unit.

The Copex has water in from the heavy rain recently so no doubt the armoured is partially submerged but surely any problem would show up on the insulation test?

The only thing I can think of is that the Isolator is faulty so when I next go back i'm going to bypass it and see if he fault clears.

Apart from that i'm out of ideas, anyone got any thoughts?

Cheers
 
the insulation tests all come back fine - +800Mohms on a 500 volt test but when I power up the installation I get 90 volts leaking to Earth from Neutral and i'm not sure why.
What tester are you using when you see the 90 volts? Make the same test again using either an analogue tester or a digital tester with a 'Lo-Z' facility.

Here's one of the many past discussions about ghost voltage;
 
90 volts leaking to Earth from Neutral

Sorry, this doesn't quite make sense. Neutral is already near earth potential. Do you mean: "There is a leak from line that raises the neutral conductor to 90V from earth?"
If so, then yes, the leak is probably normal capacitive leakage but the neutral conductor is not solidly connected to neutral because of a bad contact in the isolator. Any significant voltage on a neutral conductor especially when unloaded, indicates a faulty connection upstream.
 

Reply to Strange N-E fault on armoured cable supply to sub-main in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
388
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
971
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
Many thanks all. Very helpful to be able to bounce these things around. Was fairly happy with it all initially, but once the seed of doubt is...
Replies
8
Views
851
  • Question
There could also be a completely unsuitable junction box embedded within the wall and tiled over or just cables in choc blocks in old accessory...
Replies
6
Views
994

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top