Location
silverthorne, co
I have a 20 amp gfci pool pump breaker that trips only when the pump is off during the night. Pool pump runs fine all day. I turn pump off manually at night by using the manual switch on a Intermatic pool timer. Watch it for 5 minutes and note that breaker remains in on position. Go out in morning and breaker is tripped. Breaker is in a protected box with no water intrusion, no rain on these days etc. The only item on the circuit is the 220 pump.

Pool timer pins have been removed temporarily so we dont worry about timer clicking on.

Since timer is after the breaker and is set to off, doesnt seem the timer or the pump itself should have anything to do with the tripping.

Any ideas? Many thanks
 
As it is a 240V pump, if the Intermatic timer contacts are only disconnecting one hot leg of the power feed, the motor windings can remain live via the other leg when switched off and therefore can still trip the GFCI if there is a problem. The ground leakage from the windings could be increasing as the motor cools down, either because a small amount of moisture is then able to build up, or just because something contracts as it cools.

The logical next step is an insulation resistance test of the motor windings both hot and cold.
 
As it is a 240V pump, if the Intermatic timer contacts are only disconnecting one hot leg of the power feed, the motor windings can remain live via the other leg when switched off and therefore can still trip the GFCI if there is a problem. The ground leakage from the windings could be increasing as the motor cools down, either because a small amount of moisture is then able to build up, or just because something contracts as it cools.

The logical next step is an insulation resistance test of the motor windings both hot and cold.
Super- very helpful.. thanks lucien
 

Reply to Strange pool pump breaker tripping in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
378
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
947
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
It would be more helpful if you could tell us what the HP is on the motor since it will have to be considered a continuous duty motor since it...
Replies
1
Views
431
  • Question
Hi Gingerrubix, The fact that your previous Tenant replaced a faulty socket plate which he used for an external EV, raises an eyebrow. Also your...
2
Replies
25
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top