Afternoon all.

I've got a problem with an RCD tripping that I can't get my head round.

Upstairs lights are tripping the RCD. I switch off the MCB, but still tripping. So you'd think it was an earth/neutral fault. Nope. I remove the earth and the neutral from the board, and it trips on Live only. Very strange.

>299 ohms IR on all configurations (L/E, L/N, E/N), so no shorts.

Borrowed neutral? Nope. I wired the house 2 years ago. All been fine until last week. Also, putting the circuit on the other side of the board doesn't solve it.

Faulty RCD? Nope. Tests fine, and tried another new one just to make sure.

Anyone got any ideas?


Best regards,

E
 
Any outside lights ?
Any other trades been in.
Plumbers don't mind running hot pipes close to cables, IR may show clear untill they heat up and touch.
Or is it lecky's that run cables too close to pies lol.
Did you take all neutrals out of the bar except the circuit at fault, or just open the MCB s to the others ?

NEVER run cables next to pies. This should be a given. Daz
 
I sympathise with anyone who has a tripping RCD. To question the ability of anybody's failure to find a fault is d*ck waving of the highest order. I had a problem last early last year that went on for 6 months, and I didn't find the answer, but the customer did.

I had replaced 2 x fuseboards (3036) with RCD protected CU's. I did a complete PIR before even starting the job, that included full readings for each circuit. After I'd done the board changes I was asked to run electrics for a power shower to the 3rd floor guest bathroom.

I had this whole floor to myself so I set up complete with radio whilst I worked. It was then the RCD problem began, manifesting itself by my radio suddenly stopping. I would run down to the ground floor reset the RCD then maybe an hour or 2 later it would trip again.

Anyway I tested and commissioned the circuit and began to delve into the nuisance tripping. I retested every circuit on the board and everything looked good...separation of cicuits good, RCD characteristics good. There was no rhyme or reason for this constant tripping.

I told the customer about the problem and asked him to make a log of times it tripped. It was about a week later that I got a phone call that the RCD tripped again, in fact multiple times. There was no pattern to it. Sometimes nothing for a week and then half a dozen times in a day.

The solution was found by a young lady staying in guest bedroom of the top floor. The customer called me and said we've found the problem come over. We went upto the 3rd floor guest bathroom and my customer turned to the young lady and said "OK show him your trick"!!! She put her feet together jumped forward a foot and as she landed the lights tripped.

No doubt you've all guessed the problem. It was cable run in a joist notch held in place by a clout. Over the year the clout and eroded the neutral insulation so any pressure tripped the RCD. Now I must have tripped that RCD so many times, but I was more aware of my radio going off and the circuit it was plugged into rather than where I was walking or standing.

I read this forum often but I must say that senior posters must seem intimidating to some, as they often doubt peoples' abilities and are dismissive and disparaging to many. Oh but of course I forgot they have their fountains of wisdom from the day they were born, and never had mishaps or bad days along the way. If you've never had a carp day in your life where you been?

Yeah I get banter and all that....but please be aware that being to aggressive drives new posters away. I have no doubt Webster knows exactly what he is doing, and bouncing of peers is a great way to go. Sometimes we all have senior moments. To those superior condescending sparks on here..remember you were a tinhorn once...but at the same time we respect your knowledge...please feel free to share!!


[ElectriciansForums.net] Strange RCD Problem
 

Reply to Strange RCD Problem in the UK Electrical Forum area at ElectriciansForums.net

Similar threads

  • Question
Thank you for taking the time to help explain this - much appreciated
Replies
7
Views
779
In my opinion replacing the consumer unit and waiting to see which RCBO trips is not a good fault finding technique. If the lighting circuit...
Replies
8
Views
598
davesparks
D

Recommended Sponsor News

Exclusive Forum Offer! Free euro 2024 wall chart for first 10 responses!

Hi everyone,

We have 10 exclusive Uheat EURO 2024 Wallcharts to giveaway for Electricians Forum Members! The first 10 people to reply YES to this thread - I will message and get them sent out to you just in time for this years tournament! GO GO GO

Quickwire Now Sponsor ElectriciansForums.net

I am sure you will join me in welcoming our newest sponsors of ElectriciansForums.net - Quickwire! They have decided to join us after seeing you guys discussing their products here. Now we have an expert on board that you can chat to @Quickwire-Sam who will be happy to answer your queries!

[ElectriciansForums.net] Quickwire Now Sponsor ElectriciansForums.net


@Quickwire-Sam said "At Quickwire, we're all about speed, safety, and reliability. We're a family-run business, and every Quickwire connector is proudly made right here in the UK, ensuring noticeable quality. In short, Quickwire is the fastest connection method on the market. Whether you're an experienced electrician or a DIY enthusiast, Quickwire makes electrical connections ridiculously quick and easy. We're passionate about blending British craftsmanship with innovation. If you have any questions or if there's any way we can help, please just ask me!"

PCBWay Now Sponsor ElectriciansForums.net!!

I hope you will all join me in welcoming our newest sponsor to the forum PCBWay! You can contact their friendly people by sending a message to @PCBWay who will be happy to answer your queries.

Welcome to the community and thanks for your sponsorship!

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

PCBWay provides services including PCB Prototype and batch Production, PCB Assembly (SMT), 3D Printing, CNC Machining, PCB Design, Electronics Modules Selling, etc. We are committed to meeting the needs of global makers from different industries in terms of quality, delivery, cost-effectiveness, and any other demanding requests in electronics.

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top