Lol funny guys on here ok tell me whats going on then?

Yes i done an ir test between l/n,l/e and n/e all of which cam back greater than 299mohm.

I am getting 248v between l/n and l/e.

Do you have continuity figures for the circuit? R1, Rn or R1+Rn?
 
High resistance joint on the L (or N). Simple application of Ohm's Law. If you're not pulling any current (I imagine your megger has a high input impedance) then the voltage drop over even a largish resistance will be low, and you will measure a high voltage. Whereas anything pulling a reasonable amount of current (with a low resistance), the majority of the voltage will drop across your high resistance joint.

Hence Handyspark's question, I guess... :)
 
Thanks happysteve i looked for a joint but couldnt see any.

It might be under the floor or in the wall tho so ill prob end up rewiring it.

Or it might be in the service head, meter, isolator if fitted, a loose henley block connection.

I would put the system under some load and check the voltages all the way through the system. That will help point you in the right direction.
 

Reply to Strange things at callout in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
545
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
988
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
921

Similar threads

  • Question
When you say plus kettle, does this indicate you are needing 13A socket/s on the island and a hob supply? and then an oven supply on a tall...
Replies
5
Views
785
Seen this where T&E has been fixed with a flat bend of too tight a radius.
2 3
Replies
35
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top