Strange Ze on a TN S | on ElectriciansForums

Discuss Strange Ze on a TN S in the UK Electrical Forum area at ElectriciansForums.net

Gringoking88

-
DIY
Joined
Jun 18, 2015
Messages
176
Reaction score
58
Location
London
Hi all,

Hope you are all well.

I went to do an EICR at a small domestic property supplied by a TN S today, it is wired in singles using the conduit as CPC, however, there are no lugs for fly leads to sockets or light switches. In itself, what does this warrant, C2 / C3, there are only class 2 fittings in use?

Also, upon initial check the incoming fuse carrier was smashed and needed replacing, also Ze was 0.00 with a PFC / PSCC of greater than 10 KA. I advised the client to call DNO to replace fuse carrier, sort the earth and fit an isolator, tbf they atended within a few hours, replaced the fuse carrier, but left the main earth terminal off and said to the client call me back and I can put a clamp on it, rightly or wrong, I revisited and clamped the main earth, however, carried out the Ze again and the same reading is achieved.

Can someone help explain how and why I get that reading and more importantly, how I resolve it?

Many thanks in advance,
 

Attachments

  • [ElectriciansForums.net] Strange Ze on a TN S
    IMG_20201122_102752.jpg
    65.7 KB · Views: 50
For a start I would call back the DNO to suppy an earth Under Reg 24 they must do so, i.e. maintain an existing earth. They should have put a braided earth on with their spring tension clip. There is now way you should do that. Resolving 10ka PFC not a problem to resolve. CU is rated to 16ka, back up fuse anything from 16 to 33 Ka which covers your upstream OCPD.
 
it is wired in singles using the conduit as CPC, however, there are no lugs for fly leads to sockets or light switches. In itself, what does this warrant, C2 / C3, there are only class 2 fittings in use?


Hi, a domestic installation of metal conduit CPC is not common to me. And one that is done properly and in good condition throughout is perhaps rare. But if the conduit is properly bushed to metal back boxes and the Zs at each point is good and there is at least one solid fixing from the back box then it’s sufficient and no code is required in my view. For sockets there must be fly leads though?
 
For a start I would call back the DNO to suppy an earth Under Reg 24 they must do so, i.e. maintain an existing earth. They should have put a braided earth on with their spring tension clip. There is now way you should do that. Resolving 10ka PFC not a problem to resolve. CU is rated to 16ka, back up fuse anything from 16 to 33 Ka which covers your upstream OCPD.
I will do that as agree. I was just very surprised they said just get the electrician to do it. I was more surprised about the readings tbh.
 
Hi, a domestic installation of metal conduit CPC is not common to me. And one that is done properly and in good condition throughout is perhaps rare. But if the conduit is properly bushed to metal back boxes and the Zs at each point is good and there is at least one solid fixing from the back box then it’s sufficient and no code is required in my view. For sockets there must be fly leads though?
No Fly leads anywhere and no lugs to do so, not on sockets either, just the fixing screws to give continuity.
 
Please tell me you didn't fit an adjustable earth clamp to the lead sheathed supply cable.
I could but I would be lying, I was extremely careful not to damage the supply cable and weiging up the risks, thought it was better to an earth than no earth at all???.... Not saying I got it right but would value wiser words?
 
I could but I would be lying, I was extremely careful not to damage the supply cable and weiging up the risks, thought it was better to an earth than no earth at all???.... Not saying I got it right but would value wiser words?
hold my hands up. i've done it myself a couple of times.
 
Fitting one of those to a lead sheathed cable is extremely hazardous. Packaging on many of these clamps state they are not to be used on this type of cable, any type of cable for that matter. It is not possible to maintain a tight connection to the cable and you certainly don't want to be in close proximity should the clamp create a fault situation within the cable.
 
Fitting one of those to a lead sheathed cable is extremely hazardous. Packaging on many of these clamps state they are not to be used on this type of cable, any type of cable for that matter. It is not possible to maintain a tight connection to the cable and you certainly don't want to be in close proximity should the clamp create a fault situation within the cable.
Completely agree mate, but given the choice of no earth or an earth, double edged sword?....
 
No Fly leads anywhere and no lugs to do so, not on sockets either, just the fixing screws to give continuity.
Ok, reading Reg 543.2.7 an earthing fly lead is required in each accessory. And for safety, I would say it really should be there in an outlet. So C2 from the judge with red wine in hand.
 

Reply to Strange Ze on a TN S in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
312
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
834
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
941

Similar threads

N
  • Question
In my first sparking era (late 90's) I was always told to run a neutral to the isolator, as the chances are whoever is using the machine will...
    • Like
2
Replies
21
Views
1K
  • Question
Hi Gingerrubix, The fact that your previous Tenant replaced a faulty socket plate which he used for an external EV, raises an eyebrow. Also your...
2
Replies
25
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top