jpmiff

Hi all,
been doing some testing on my house to get some practice, whilst doing an IR test on a ring circuit 2.5mm t&e i get >299M LN, >299M NE, when i test LE the reading starts at 5M, leave the test running and the reading continues to grow, went upto 50M before i stopped the test:confused:.
R1 end to end 0.58 ohm,Rn end to end 0.6 ohm, and R2 end to end 1 ohm.
i have found a section of cable which is causing the low reading and will change as soon as.:rolleyes:

What would cause the test reading to continue to get higher the longer you leave the test running?

thanks all
 
generally speaking damp could cause a reading like this
is this possible in your house?
remember the reading is well over the minimum so if it is a load of grief to replace the cable in question its fine to leave it
 
Its an upstairs ring circuit, would not expect any damp and no signs of any.It means emtying a bedroom to get the boards up to replace the cable:(.not sure what to do

thanks for the quick reply
 

Reply to strangeIR reading in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
275
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
773
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
779

Similar threads

I was at the other end of the results spectrum today. As I was driving home I had a call from my "Mrs Richards from Fawlty Towers" lady, very deaf...
2
Replies
20
Views
1K
Having some issues with my companys fluke 1662/1663 tester. Zeroing 2 leads for continuity test we get the value 0.08 which is expected. The issue...
Replies
0
Views
254

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top