Struggling please help
daws124
A 230v single phase double wound transformer has an output of 20A at 110v
Determine the
kVA rating....
Primary current...
Transformation ratio...
Please explain my brain is mush! Thank you.
Forget 41 amps as primary current. Your turns ratio is correct but the other 2 are wrong. Reconsider power equals volts multiplied by amps. Power in equals power out in this simple case.
Upvote 0
Dam :( ha! So basically it's 110x20=2,200 so 2.2kVA?? So if that's right? The primary current would be 1000x 2.2kva/230v...?? My head is going to pop! This is helping thank you
Upvote 0
Determine the
kVA rating....
Primary current...
Well done you have put the effort into it and (with some assistance) have got the answers!
kVA is the power and for a 100% efficient system is (volts/1000) * amps
therefore kVA is (110/1000)*20 = 2.2 kVA
Using Archy's equation rearranged Primary current, Ip, is (Is*Vs)/Vp = 110*20/230 = 9.56A
Turns ratio is Vp/Vs =230/110 = 2.09
Done
Upvote 0