At the termination of an MI cable, which test range should be used for a 230 volt circuit. What result should be expected?
 
I'm guessing insulation resistance at 500volt and the reading should be > 200M or that depends on which tester you use. The answer could also be >1M as that the lowest acceptable value in BS7671
 
Ir test/500v Line to outer sheath, Neuteral to outer sheath and Line to neuteral. you are looking for a minimum reading of 1Mohm but ideally a minimum of 2Mohm
 
not o IR test the hbigher the resisance the better. remember, if you reasd the last posts, you are measuring the resistance between L/N and E. the ideal reading would be infinity as the inly connection between these is the mineral insulation. you are doing the test to determine 1. if the insulation has got damp. 2. you have not ballsed up and shorted out the conductors when you terminated it. end of lesson.
 
so 1.0 is the as lowest.....the higher the number gets the worse the reading is?


You meed to get this right mate, its not 1.0 its 1Mohm as in 1 mega ohm !!

So 999 ohms would be a fail.

If a Pyro has been terminated correctly and depending on what machine you use to test you should expect something like

>200Mohm

that means "overange" so its is a figure greater than the tester can measure and >200Mohm means Greater than 200 mega ohms
 
1M ohm =1Mega ohm=1Million ohms .......IR test bigger is better

I'm still training too...get yourself a copy of the unite handbook for testing (the yellow one) its only 7 quid it is a really useful book
 
Last edited by a moderator:
ir test is to ensure the circuit has no dead shorts in it or low ohm faults normally you will get a reading of >999 or whatever the highest reading is however anything more or equal to 1
altho if you get anything between 1-2 you will need to investigate further.
 
so 1.0 is the as lowest.....the higher the number gets the worse the reading is?

you might be mixing the higher / lower values up with continuity testing using a (low resistance ohm meter) when you are testing insulation resistance as said the value is healthy when high. when testing continuity the value would want to be a low one in (ohms)
 

Reply to Stuck on mock exam question..... in the Talk Electrician area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
381
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
961
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
It was a one time ÂŁ19.99 fee. I'll be reaching out to them though to get that back. It was the only online extensive bank of questions that I...
Replies
7
Views
1K
In TN-S systems, you shouldn't isolate the neutral in a 4-pole isolator. Connecting neutrals to a dedicated terminal is acceptable and safe...
Replies
4
Views
662

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top