re-jig the feed to the sub from it's own dedicated MCB. (6mm cable on a 40A. RCD protected??). but that's not in your remit of doing a EICR. quote it.
Only if it says that in the extent and limitations.I'd say that your responsibility ends at the socket.
I don't believe so as the item in question is outside the remit of BS7671.Only if it says that in the extent and limitations.
Maybe not, but I’d put it in there anyway because mr and Mrs miggins won’t know that.I don't believe so as the item in question is outside the remit of BS7671.
Maybe so, but if the householder is aware of another consumer unit, feeding several circuits, they may expect that to have been inspected and tested. So for the sake of clarity I would include it as a limitation.I don't believe so as the item in question is outside the remit of BS7671.
Eloquently put!Maybe not, but I’d put it in there anyway because mr and Mrs miggins won’t know that.
Like wiseMaybe so, but if the householder is aware of another consumer unit, feeding several circuits, they may expect that to have been inspected and tested. So for the sake of clarity I would include it as a limitation.
If this was to be treated as part of the fixed wiring, then I believe (though stand to be corrected) that a 13A BS1362 fuse will protect a cable rated at =>18A.Something doesn’t seem right with me classing it as only a C3 either!
The loading of the air conditioning unit shouldn’t matter should it? If it pulls more than 13A the plug top would blow.
My concern is the 1.5mm flex cable that is on the plug top could overheat if too much current is drawn .. but the fuse would operate if there was any danger? Or am I wrong in assuming the 1363 fuse is adequate?
Is that 20A calculated from the Kw output of the Unit?Thank you all for your inputs so far.
Is there anyone who disagrees with a C3?
The sub-board had 4 circuits:- 2 x Radial socket (each supplying one socket) 1 x Lighting (supplying 2 wall lights) and 1 x 20A air conditioning unit.
you should not be posting such long dissertations after beer o'clock. ???Everyone is being fooled by the appearance of the plug and socket, due to familiarity with the socket outlet as a means of connection for portable appliances. The plug here is not part of a portable appliance, so the dedicated plug-and-socket arrangement becomes a piece of switchear along the run of submain from main DB to conservatory DB. Consider it to be equivalent to an FCU, but using withdrawal of the plug to achieve double-pole isolation. No-one would argue that a permanent circuit fed from an FCU is not part of the electrical installation, surely?
Then, the question is whether as a piece of switchgear, the plug-and-socket is adequate for the purpose. Is its current rating high-enough for the design load, for example,? What about the COP guidance that limits the BS1363 plug earth pin to a maximum design leakage of 3.5mA? You would not really want that limitation on a submain. Used as an isolator, it also switches the CPC, which it is not supposed to do. Overall, I see this as an inappropriate piece of switchgear on the submain and would code it according to its shortcomings in that role.
For anyone still convinced that connection via a plug excludes the conservatory from the installation, consider a theatre-lighting system where all the circuits are patchable. Every dimmer channel (=DB way, which might number dozens or hundreds) terminates in one or two socket-outlets, often directly adjacent to the DB. Every installed circuit cable leading off around the building begins with a plug that can be placed in any of these outlets, like a telephone exchange. Would you then consider that none of the installed wiring is part of the installation?
Note that in the theatre patch panel, the CPC of all the circuits connects to the MET so that it does not rely on the contact of the plug and socket, and remains connected with the plug out. The plug and socket CPCs are also connected for completeness.