Bbb p121What book is that in mossep?
Thanks, wasn’t taking the pi$$ I’m still on the byb and couldn’t find it...Bbb p121
Its in the BYB too, not sure what page though but probably a similar reg number.
Thanks spoon I’ll be in there later.537.1.4 A main linked switch or linked circuit-breaker shall be provided as near as practicable to the origin of every installation as a means of switching the supply on load and as a means of isolation.
A main switch intended for operation by ordinary persons, e.g. of a household or similar installation, shall interrupt both live conductors of a single-phase supply.
BYB page 154
Thanks mossepIts in the BYB too, not sure what page though but probably a similar reg number.
Its OK.. I still haven't booked my 18th exam. Don't think I'm gonna get a place before Jan eitherThanks, wasn’t taking the pi$$ I’m still on the byb and couldn’t find it...
537.1.4 A main linked switch or linked circuit-breaker shall be provided as near as practicable to the origin of every installation as a means of switching the supply on load and as a means of isolation.
A main switch intended for operation by ordinary persons, e.g. of a household or similar installation, shall interrupt both live conductors of a single-phase supply.
BYB page 154
Which is open to interpretation ... A main switch per fuseboard and per switch fuse could serve to provide the necessary isolation.
If not hundreds of thousands of properties could be deemed dangerous