Greetings.
I am wiring a large garage for a friend.
The wiring will be done in singles enclosed in 25mm round conduit running all the way around the garage in the roof space with T-Pieces put in place that will allow cables to drop from the roof space in 20mm conduit to the switches and sockets.
The whole thing is visible with no concealed cables in walls etc.
I have bought a Wylex eight way dual RCD board and will use three of the ways for lighting, sockets and an additional radial for the fridge and freezer.
The lights and sockets will be RCD protected but the fridge and freezer will not, the socket will be marked fridge freezer only.
The supply cable is protected by a 32 Amp type B MCB at the main house and the cable is 4mm SWA with one core used as the CPC, the armouring is earthed at both ends.
There is are no extraneous metal parts in the garage, no water etc and the supply is TN-S.
Because the Sub board will eventually have a few more circuits added, probably lighting, I will use diversity to assess the overall load, when I add up all the MCB's on the sub board they will probably total more than 32 Amps.
Does this sound Ok, having a non RCD protected dedicated circuit for the fridge freezer in a garage and also using the principal of diversity on a sub board?
I cannot think of any good reason why my approach is wrong but I am wondering if anyone can see a fault in this design.
Thanks very much.
I am wiring a large garage for a friend.
The wiring will be done in singles enclosed in 25mm round conduit running all the way around the garage in the roof space with T-Pieces put in place that will allow cables to drop from the roof space in 20mm conduit to the switches and sockets.
The whole thing is visible with no concealed cables in walls etc.
I have bought a Wylex eight way dual RCD board and will use three of the ways for lighting, sockets and an additional radial for the fridge and freezer.
The lights and sockets will be RCD protected but the fridge and freezer will not, the socket will be marked fridge freezer only.
The supply cable is protected by a 32 Amp type B MCB at the main house and the cable is 4mm SWA with one core used as the CPC, the armouring is earthed at both ends.
There is are no extraneous metal parts in the garage, no water etc and the supply is TN-S.
Because the Sub board will eventually have a few more circuits added, probably lighting, I will use diversity to assess the overall load, when I add up all the MCB's on the sub board they will probably total more than 32 Amps.
Does this sound Ok, having a non RCD protected dedicated circuit for the fridge freezer in a garage and also using the principal of diversity on a sub board?
I cannot think of any good reason why my approach is wrong but I am wondering if anyone can see a fault in this design.
Thanks very much.