Hi

I have reviewed a few posts around this subject, but my question is not covered. I know that the Submain Earth has to be sized on the DNO incomer, not on the submain to the external building itself. My question is if I need two main bonds in the submain building, for example one for ground fed metal pipe for water and ground fed metal pipe work for gas, does that mean the equivalent earth sizing of the armoured / extra conductor in the armour, must also be sized to take account of 2 x 10mm or just one 10mm (example assumes TNCS with 25mm Line. Or is there something in the regs that assumes one fault to earth only and not multiple?

Thank you.

John
 
as long as the SWA is 3 core. the cpc is adequate for bonding, the steel armour is superflous. but must tbe earthed, as you know.
 
as long as the SWA is 3 core. the cpc is adequate for bonding, the steel armour is superflous. but must tbe earthed, as you know.
on one specific armouring is used (TPN 4 core cable only) for CPC (installed a long while ago). There is another sub-main in this building which does use a core for CPC. Same size too. Was thinking of joining both armouring and the SP CPC and creating a sub MET in the building and then running the main earth from this Sub MET so shared across two sub-mains for both supplies. I should state that the Single Phase board is supplied via a manual change over switch to be fed via generator in the event the site mains fail.
 
It won't be a Sub MET (MAIN Earth Terminal), it would be an EMT (Earth Marshalling Terminal). Common practice on a lot of sites to use this method.
 
It won't be a Sub MET (MAIN Earth Terminal), it would be an EMT (Earth Marshalling Terminal). Common practice on a lot of sites to use this method.
Thank you. By the way what is the best way of knowing the exact size of the DNOs supply conductors? Would they know if i called or have i got take it apart and measure?
Thanks.
 

Reply to Sub Main Armouring Earthing Question Combined CPC and Main Bond in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Sticky
  • Article
Wicked I've just actually looked through it and it's very smart. Some good stuff in it. There's a tile association company that do a magazine...
Replies
2
Views
274
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
269
  • Article
Hi everyone, Another weekend, another sale! Get ready for colder days with Haverland Radiators, combining efficiency with modern design. Keep...
Replies
0
Views
350

Similar threads

  • Question
Why would the RCD fail … yes it can happen but then it may not. Without it you have no protection on the TT System
Replies
36
Views
4K
  • Question
By retired electrician, I mean that I have retained my ticket but no longer do installation work. Thanks for the clarification. I missed that it...
Replies
2
Views
444

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top