Thanks needasparks.
Just been on to the doncaster website as i was unsure of the csa of the cpc of the 10mm T&E and as it comes out at 4mm. My plan will be to running an additional 6mm cpc.



Edit
Sorry for the late response but i could not reply posts till today
 
Last edited by a moderator:
if your running trunking why don't you wire everything in singles and use MCB's?
if there is a suspended ceiling why don't you use cable tray above the ceiling?
 
We had a drum of about 70m of T&E so couldn't justify the £200 spend on singles. As for the trunking, there is plenty space as it is 100mm x 100mm and about 20% full.
 
We had a drum of about 70m of T&E so couldn't justify the £200 spend on singles. As for the trunking, there is plenty space as it is 100mm x 100mm and about 20% full.

Save your T&E for another job and use singles on this installation. Your already having to supply a separate single CPC conductor, so bite the bullet and do things properly by using the right installation cable....
 

Reply to the thread, titled "Sub main board question" which is posted in Electrician Talk | All Countries on Electricians Forums.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Daily, weekly or monthly email

Back
Top