Hello Good Folks!
*
I am a humble domestic spark that is not the most experienced (although not a Electrical Trainee!). I tend to do board changes and smaller stuff. An existing customer has asked me to rewire a couple of flats, one of the flats already has a new sub main ran in by the builder. The cable looks to be YY type, NOT armoured, is defo 16mm 3 core, but looks to have no mechanical protection and is prob <50mm from wall surface. The runs are around 8m for each flat.

YY cable is listed as a control cable rather than a power cable, so if this cable is indeed YY then is it suited as a sub main cable?* There is writing on the cable but I could not get through to investigate due to room full of carp. I will do so in due course.
*
16mm YY cable is good for a max of 82A (these are one bed flats with kitchen/lounge as one room (so demand won’t be heavy)). DNO should be happy with 16mm I would assume if 60A supply requested. There is a separate 16mm earth also ran in.

So my question is *would a 100mA RCD up front provide sufficient protection or should the YY be replaced with SWA. No intake is present as of yet as being installed soonish I believe.

For the other flat I was going to run in 16mm 3 core SWA with a KMF up front. I am going to ring NAPIT technical on Monday but I know for sure they will probably say don’t put a 100mA up front despite the fact that there will be two 30mA at board.
*
Thoughts welcome please (even OJL!!)

Thanking You!
 
Thanks for responses.

Consensus is replace the cable. So that's what I will quote for. Wasn't that happy when I saw what was installed anyway. Yeah, from the tech spec I saw the YY didn't sound the ideal choice! Although it may not be YY. But it is definately unarmoured.

And thanks for the heads up re the kmf and swa; always good to know.

Thanks again.
 

Reply to Sub main cable type in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
388
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
970
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

You would treat it as a TT installation.
2
Replies
29
Views
2K
Yes the first bit is just standard wiring, TNS lead cable into cut-out, cut-out to meter, meter to DP isolator, top of isolator is sealed as per...
Replies
8
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top