been asked to supply a site containter which is going to be used as an office. the run is 125 metres long. 2 fluorescents, a few sockets and a 3k heater in the office. sockets are going to be used for computer only. the swa is going to be run on the perimeter fence clipped direct. I'm thinking 10mm on a 32amp breaker. any opninions?
 
been asked to supply a site containter which is going to be used as an office. the run is 125 metres long. 2 fluorescents, a few sockets and a 3k heater in the office. sockets are going to be used for computer only. the swa is going to be run on the perimeter fence clipped direct. I'm thinking 10mm on a 32amp breaker. any opninions?


Have you done volt drop calculations?
 
I'm just about to catch a train but just use the usual mV/A/m with values from table 4D4B with a design current (Ib) of say 20 Amps and that'll give you an idea.
 
Also remember that if your Ib value is significantly less than the current carrying capacity of the cable, the calculation will be artificially high as it is based on max conductor operating temperature (full load).
 
ok so u mean i should work it out using ib as whatever size breaker im going to use ? apologies dont do these calcs often
 
remember its the lighting that needs to be considered only 6.9VD max

just done a job in a stables, small stables was 70m from origin to carry 20A max load, i used 16mm SWA this gave me a VD of 3.9v to my sub main CU under full load conditions, then around 2v drop for my biggest/longest lighting circuit 5.9vd alltogether

so there is a small window for additions on the install but not much

If you go by the book even 16mm is gonna be over 7v to end of sub main(in the real world this would probably be fine, but if its not..........)

Looks like its 125m of 25mm SWA.....ouch!!!
 
Last edited by a moderator:
OK, so here's something that's always bugged me. How come it is that I have to install (hypothetically) a run of expensive 25mm to carry 50 A for 60m (or whatever the calc would be) but the DNO can lay in a 16mm concentric to deliver me 80A from a spur 100yds up the road.

What magic do they have in their screwdrivers that is missing from mine?
 
OK, so here's something that's always bugged me. How come it is that I have to install (hypothetically) a run of expensive 25mm to carry 50 A for 60m (or whatever the calc would be) but the DNO can lay in a 16mm concentric to deliver me 80A from a spur 100yds up the road.

What magic do they have in their screwdrivers that is missing from mine?

^^I have allways wondered exactly the same

Allthough, i actually carried out a test on my summer house in my garden with a 6mm SWA run, loaded it up with 2x 3kw heaters, calculated the VD then measured it and it wasnt that far out at all
 
OK, so here's something that's always bugged me. How come it is that I have to install (hypothetically) a run of expensive 25mm to carry 50 A for 60m (or whatever the calc would be) but the DNO can lay in a 16mm concentric to deliver me 80A from a spur 100yds up the road.

What magic do they have in their screwdrivers that is missing from mine?
wondered that myself, come on Tony put us out of our misery
 

Reply to Sub main help in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
350
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
898
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Regulations notwithstanding, the only thing in those pics that is likely to be affected by sheep is the trailing flexibles on the ground from the...
Replies
29
Views
2K
  • Question
Many thanks all. Very helpful to be able to bounce these things around. Was fairly happy with it all initially, but once the seed of doubt is...
Replies
8
Views
837

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top