Domestic, three phase supply, one phase to each of three consumer units. Two consumer units are local to the intake, the third CU is on the first floor.
Currently the first floor CU is fed via a fused isolator at the intake. The replacement CU will be rcbos. However, we thought this submain was SWA, but discovered today that it is split concentric. Soo, looks like we now need to apply additional protection to the submain as it is buried in the building fabric.
We want to achieve discrimination with the 30mA rcbos in the new board, so is a 30mA time delayed rcd replacing the switch fuse acceptable in this situation?
Also, we would prefer to provide overcurrent/short circuit protection via a fuse, as opposed to an mcb. I recall there are fuse holders which fit on a DIN rail, but not sure of make/spec - anyone point me in the right direction?
Oh, it’s TNS, Ze of 0.34.
TIA
 
if its split concentric then the neutral is only really actually single insulated isn't it..... and we normally give single insulated conductors that arent in trunking etc a C2. Imo I wouldn't want to leave it personally
 
if its split concentric then the neutral is only really actually single insulated isn't it..... and we normally give single insulated conductors that arent in trunking etc a C2. Imo I wouldn't want to leave it personally
The conductors will only be insulated once regardless - the sheath is there to provide mechanical protection to protect the insulation - not to afford an additional layer of insulation. (That's why Pyro can get away with having an earthed copper sheath - the magnesium oxide only provides one layer of insulation.)

However the neutral conductors in split concentric cable will be both insulated and sheathed. The problem is that there is no guarantee you won't contact neutral (a live conductor) rather than the protective conductor when piercing the cable unlike with SWA.
 
[ElectriciansForums.net] Sub main protection, views please.
Split concentric should be terminated with a 3 finger boot and heat shrink on the conductors.
 

Reply to Sub main protection, views please. in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
388
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
970
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
Many thanks all. Very helpful to be able to bounce these things around. Was fairly happy with it all initially, but once the seed of doubt is...
Replies
8
Views
851
  • Question
Thanks for all comments still debating how to solve this, i personally would install MCB, having an idea the cable is installed under...
Replies
11
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top