Sub main | on ElectriciansForums

Discuss Sub main in the Australia area at ElectriciansForums.net

Joined
Sep 30, 2009
Messages
93
Reaction score
0
Location
Dartmoor
Hi All,

Just a quickie,

On a job at the mo. A replacement c/u , rewire shower and some sockets etc.

The c/u is near the kitchen fed by a 16mm t+e sub main. The sub is fed from a switch fuse in the hall way. Prior to the switch fuse is a older 100ma RCD. you know the big grey and black fellas.

My question is should i leave the older RCD in to protect the sub (subject to test). The c/u will have 2 30ma RCD's installed so discrimination will be ok.

Should I remove or leave it if it checks out ok.

Feedback welcome

G
 
There wont be any discrimination between the 100mA RCD and the 2 30mA RCD's in the CU......unless it's a time delayed "S" type one.

Depending on how the sub-main is installed it may need RCD protection of the 30mA variety though.
 
Ok, if the T+E sub is buried in the wall less than 50mm and not in earthed mateallic conduit etc etc then it will need additional protection by 30mA RCD.

If it's surface run in it's entireity though in pvc trunking for instance, then it would not need the additional 30mA protection. If it's a TT system though then it would need an RCD up front regardless of install method i.e a 100A 100mA time delayed type.
 

Reply to Sub main in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
223
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
683
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
625

Similar threads

  • Question
Many thanks all. Very helpful to be able to bounce these things around. Was fairly happy with it all initially, but once the seed of doubt is...
Replies
8
Views
819
Regulations notwithstanding, the only thing in those pics that is likely to be affected by sheep is the trailing flexibles on the ground from the...
Replies
29
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top