H

hawkomontana

Good day all!

my mate has asked me to install a new sub mains directly below the main cicuit board because he only has 1 way left in the original board.

In the sub mains board he requires a double oven rated at 10kw on a 40A breaker, a single oven rated at 9kw on a 40A breaker and a hob rated at 7kw on a 32A breaker all on there own individual circuits

My question is what size MCB do i need in the main board to feed the sub board?

cheers lads!
 
don't feed from MCB in main board, split tails in henly blocks so you are feeding your new board direct from the meter, in parallel with the main board. your new board and tails will then be protected by the DNO's 1361 fuse. don't forget to fit RCD in your new board!
 
applying diversity for cookers, to nearest round figure, your load capacity is approx. 58A. hate to have to pay your mate's elec. bill. is he gordon ramsay?
 
I was gonna do it with new tails fae a couple of neutral block spliters but my mate has already bought all the material and he just wants it done in the same manner as the 1 he has for his garage socket and light?
 
Haha i know, he's just got the new kitchen and its a total beast, Got the same calculations for diversity.

What size RCD should i go with? because he doesn't know if he will add anymore circuits to the remaining 2 ways left in the sub board (5 way sub)
 
100A 30mA RCD. do the job right, not how your mate says do it. you're the expert. if anything goes wrong, it's your head on the block, not his.!!!!!
 

Reply to sub mains board? in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Hi everyone, If you are looking for reliable EV chargers, check out our top-rated selection at E2GO! âš¡ Please note that all EV Chargers and...
Replies
0
Views
224
  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
1K
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K

Similar threads

I generally thought double stack boards were more for situations where a portrait design is better suited to the cupboard - you still generally...
Replies
4
Views
500
Question 1 do you prefer buttered, salted or sweet salted? I'm guessing salty 😜 1. Auto range multimeter (used on mains before when testing the...
Replies
2
Views
715

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top