Lionscourt

I’ve recently run a supply to a garage and I had a question concerning the earthing. Here is the situation:

TT supply to house.
Supply goes into a time-delay 100mA RCD before it splits.
This then goes through a sub-mains isolator at the house.
3-core SWA runs about 60 metres to garage.
17[SUP]th[/SUP] edition consumer unit in the garage.
New earth spike installed for supply at the garage.

So, my question: Should the SWA section be connected to earth at both ends, or only at one? Is there a reason I would NOT want to connect the earth at both ends?
 
Hi
As it's a TT system at origin no problem connecting SWA earth at both ends, as mentioned before would help your earthing value. But if your origin earth was PME for example, then the SWA wire from origin should be earthed but not be connected to the consumer unit in the Garage, that should be earth free of PME, then the earthing arrangment for the Garage would become TT from the earth electrode allready installed.
 
Hi
As it's a TT system at origin no problem connecting SWA earth at both ends, as mentioned before would help your earthing value. But if your origin earth was PME for example, then the SWA wire from origin should be earthed but not be connected to the consumer unit in the Garage, that should be earth free of PME, then the earthing arrangment for the Garage would become TT from the earth electrode allready installed.
why??? what's wrong with the PME in the garage?
 
Nothing in princible, but the example above, running 60 meters and a new consumer unit to a garage could require a bond to a water supply or any other extraneous conductive parts therfore that could introduce a potential back into the PME zone. If the cable was 3 core 10mm then bonding requirments for 100amp PME supply would be ok
 

Reply to Sub-mains earthing question in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
285
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
789
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
810

Similar threads

You would treat it as a TT installation.
2
Replies
29
Views
1K
  • Question
Many thanks all. Very helpful to be able to bounce these things around. Was fairly happy with it all initially, but once the seed of doubt is...
Replies
8
Views
824

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top