Submain Earth/Bonding question? | Page 2 | on ElectriciansForums

Discuss Submain Earth/Bonding question? in the UK Electrical Forum area at ElectriciansForums.net

F

Flakey

Hi guys/girls

Just some clarification needed. I have an house where there is sub board in the garage , and also a boiler in the garage. The water copper pipe that connects to the boiler is continuous from the house. I am aware of the exporting PME situation so plan to drop out the 3rd core of the 10mm swa that is feeding the board as well as the glanded armour currently connected to the sub board and TT the garage then bond services to the garage from MET in garage. What would be the best course of action with regards to the pipe being connected to the house as well as the garage? Would a length of plastic pipe be suffcient to to seperate both zones. Also where would be the best place to insert the plastic bit of pipe. for example before it leaves the house or anywhere?

Thanks in advance
 
Use the 10mm earth inside the swa to connect from house MET to EMT in garage and from there 10mm bond to pipe. Youre very lucky to find a 10mm 3core in place underground if only every outbuilding was like that. When getting telephone calls about armoured cables to garage/shed if you suggest to the customer to bung a 10mm 3c in this will usually save alot of drama when you come to connect up and future proofs the install for minimal extra cost.
 
sorry no actual input to give but was wondering if the existing boiler is powered from a supply direct from the house and therefore is earthed via the house supply with presumably the copper piping mechanically connected to this earth. I have no idea if this has any implication with regard to your bonding of pipework to your new garage supply.
 
sorry no actual input to give but was wondering if the existing boiler is powered from a supply direct from the house and therefore is earthed via the house supply with presumably the copper piping mechanically connected to this earth. I have no idea if this has any implication with regard to your bonding of pipework to your new garage supply.

The metal pipe may be earthed, but as it is a re-appearing metal pipe it needs to be bonded as per Chapter 54. Sorry haven't got the reg no, as don't have BS7671 with me :)
 

Reply to Submain Earth/Bonding question? in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
433
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
4-5 hours for 150? no chance, this is 2024, 150 for 2 hours maybe, that said an hour seems pretty quick, not sure he did the job right
2
Replies
23
Views
2K
  • Article
This is an RSS feed of thread: Best way to connect 10mm plastic pipe to 8mm micro bore Content of the thread: Hi all fitting new radiators and...
Replies
0
Views
263

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top