If I'm running a submain on a TT system in SWA then do I need to provide RCD protection for the submain? The cable is 4mm with an approx 30m run buried in the ground. Can I get a 32A switched fuse with 30 ma time delay anywhere? Obvs need to provide discrimination with 30ma RCD in the outbuilding.
 
you don't need RCD protection for the SWA. what you put in the sub-main is protection , if required, for the sub-main circuits.
 
SWA cable does not need RCD protection, no matter what the earthing system is. it's your sub-main circuits that require RCDs.
 
as it's a distribution circuit, the dis. time will be 5 secs., so hoefully the fault current will be sufficient ( depending on the Ra, of course ).
 
Not too difficult to achieve, if you know what you're doing!! The problem in the UK, is this almost total acceptance of the crazy numbty 200 ohms as mentioned in BS7671 and OSG's as being the value to aim for!!

Never even mentioned the 200 ohm bull, but in all honesty, do you think that on this job, the value of Ra is going to be low?

I don't somehow
 
If that was the case then no 5 secs is fine but not come across a TT system with a low Ra yet. But I'll keep looking


I know of more than just a few domestic TT systems in Essex, that are below 1 ohm, and in some cases, with better than the local towns DNO TN-S values!! Commercial and/or industrial made roded ground fields, are very rarely in excess of 1 ohm... As i said the biggest problem in the UK is this numbty 200 ohm malarkey and using thin twigs for earth electrodes. I'd never even heard of them before coming on UK electrical forums, and still to this day, haven't seen one in the flesh so to speak!! Only relatively recently have i seen a 1.2m 5/8'' rod, i'm used to seeing and using 2.4m and 3.2m rods.... lol!!
 

Reply to Submain on a TT in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
551
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
990
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
922

Similar threads

totally agree
Replies
12
Views
2K
It's not the same scenario, though. Tails more than 3mtrs can be overcome by using a fused switch and rcd board, whether the earthing system is...
2
Replies
18
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top