Good morning All,

Sorry for posting another sub main question but i have searched various posts and cannot find a definate answer.

I need to install a submain out to a brick built outbuilding which will be used for injured/unwanted ferret rehab. Building has no extraneous conductive parts and main supply is pme.

My plan is 32A rcbo in house consumer unit, 9 metre run of 6mm t&e through floor joists to galv box on outside wall. 6mm 3 core SWA from galv box to outbuilding 11 metre run buried under footpath and them fixed to garden wall. 2 way CU in outbuilding with main switch, 16A supply for sockets and 6A supply for lights. All in galv conduit to make it ferret proof.

My question is, would i be better off having an mcb at the house end and rcd main switch in the sub board? I feel the submain cables would be better having rcd protection but as i can comply with greater than 50mm deep at all points, i am starting to doubt my plan. Any thoughts?

ATB

Chris
 
This was the reason for my "optimistic",on Tels post...the schemes used to make you cross your fingers and promise to think about maybe trying,for the T&I,but not applying anything which could be cheque-stopping;)

I think most of the CPS's require some sort of acceptable electrical qualification. At my first assessment, the assessor wasn't interested in my boy scout awards for whittling and/or lying, but was keen to have a look at my dusty apprenticeship indentures and wax seal.

OP, give one of those schemes a bell and ask. All I would say, when I decided it might be a fun idea, and do some sparkying in my semi-retirement, I went and did a 2391. Money well spent, as I never previously seen any test equipment, other than a Drummond Test Lamp. :)
 
Thanks to all for your advice and input. All this talk of schemes has got me thinking. It may be worth a go, who knows what the future holds and maintenance in the motor industry isn't exactly secure at the moment. I will definately be looking to do the 2391 this year if a can find a way of working it round family and shifts.

With regards to the housing of the ferrets, they plan to have 2 indoor bed areas within the outbuilding with holes knocked through to outdoor runs. There will also be an indoor pen with a covered play pen style run and them some smaller hutches to act as sick bays. The sockets will mostly be located by the hutches for running heat lamps/beds (max 2) . No sockets will be located within any of the actual pens. They have certainly thought the layout through and know exactly what they need.

Thanks again.

Chris
 
Thanks to all for your advice and input. All this talk of schemes has got me thinking. It may be worth a go, who knows what the future holds and maintenance in the motor industry isn't exactly secure at the moment. I will definately be looking to do the 2391 this year if a can find a way of working it round family and shifts.
Chris

Bizarre, that's exactly what caused me to quit the industry in 1984.
 

Reply to Submain, RCD protection. in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
357
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
910
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

totally agree
Replies
12
Views
1K
L
  • Question
My Understanding is the 6 Months interval is IET Guidance and this wording is incorporated onto the label which is a requirement in 514.12.2 where...
Replies
9
Views
665

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top