Just been to see a job where I would need to replace a FCU with a RCD FCU as its to supply a fan heater (1kw) in the bathroom. Easy I hear you say but...
the existing FCU is in the adjacent kitchen and its the first spur off the ring and there are 2 more sockets linked off the FCU (not through the FCU) making 3 points off the ring as spurs of spurs.
Thought about using the existing FCU to "control" the new RCD FCU, and the 2 sockets, but the existing sockets are for the fridge (0.5kw) and the washing machine (3kw) making the possible load about 4.5 - 5 kw (worse case) so the FCU would almost certainly blow fuses on a regular basis.
Extending the ring to the FCU isn't really on as it would mean disturbing their new tiling in the kitchen!
Any suggestions please!
Thanks