That's about protective devices, it certainly doesn't refer to selection of under rated accessories?


I think you need to take a break and cool off.

Just relax and re-read what you have said and the responses, then think about it, it appears like you are reacting rather than analysing.
 
Since the advent of plastic, self extinguishing, isolators / accessories, Yes, many times.
Moreso on circuits with a protective device that matches the Isolator rating, or even less, than those where it didn't.

You've reported your concerns, they've been dismissed, that's it as far as you're concerned.
Having re-read your post I understand what you're saying about reporting my concerns & I apologize unequivocally for my somewhat surly reaction. :)
 
Last edited by a moderator:
That's funny, I just haven't seen anyone post anything that makes sense, you were doing ok though Julie until you quoted a completely irrelevant regulation.


Ok, let's try this

You have a cable capable of 20A on a 10A load

If I fit a 40A MCB, is the cable undersized, or is the MCB over sized?

If you say it's the MCB that's too large then 432.3 would be appropiate

The standards always work from one direction only.

They don't put the point in both directions

There isn't "1.2.3.4 :equipment must be suitable for the Voltage of the system" followed by the opposite viewpoint "1.2.3.5 : A Voltage unsuitable for the equipment must not be used"

It is necessary only to confirm one point of view.
 
Ok, let's try this

You have a cable capable of 20A on a 10A load

If I fit a 40A MCB, is the cable undersized, or is the MCB over sized?

If you say it's the MCB that's too large then 432.3 would be appropiate

The standards always work from one direction only.

They don't put the point in both directions

There isn't "1.2.3.4 :equipment must be suitable for the Voltage of the system" followed by the opposite viewpoint "1.2.3.5 : A Voltage unsuitable for the equipment must not be used"

It is necessary only to confirm one point of view.
You've lost me...
 
You've lost me...

Your thought, that the isolator is undersized @ 20A, is based on the fact that the protection is 32A

This is EXACTLY the same as saying the protection @32A is oversized as the isolator is only 20A

The regs only need to cover one point of view as the other is automatically covered!
 
IEC standard 60947-3 (same BSEN number) which covers switch disconnectors or isolators will tell you that they must be designed to withstand fault currents flowing through them until the protective device operates.

From what you have discribed there is no problem with the way the circuit has been installed.
 
Your thought, that the isolator is undersized @ 20A, is based on the fact that the protection is 32A

This is EXACTLY the same as saying the protection @32A is oversized as the isolator is only 20A

The regs only need to cover one point of view as the other is automatically covered!
Not really, the circuit supplies 2 split units each drawing around 12A so it has been designed as a 32A cct for that reason. I see what you're getting at but this has been designed as a 32A cct & is wired in 4mm singles. The isolators that have been fitted are there because of the availability of the correct parts in the location I'm in.
 
Not really, the circuit supplies 2 split units each drawing around 12A so it has been designed as a 32A cct for that reason. I see what you're getting at but this has been designed as a 32A cct & is wired in 4mm singles. The isolators that have been fitted are there because of the availability of the correct parts in the location I'm in.

OK, but your view is that the isolators are undersized @20A, based on the protection device of 32A. This is exactly the same as the protection device is oversized @ 32A compared to the 20A isolators as far as the regs are concerned; 432.3 details why this situation is permissible.

As long as it's a fixed load and it has fault protection, it is compliant

If these same isolators supplied multiple outlets, then it's not a fixed load and your point would be valid as someone could just plug in more loads resulting in overloaded isolators.
 
The what about 20AX switches on a ring final circuit with a 32 amp protective device? Millions of homes in the UK have this set up with no adverse effects.
 

Reply to Suitability of circuit accessories. in the Commercial Electrical Advice area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Merry Xmas to all :D
    • Friendly
    • Like
Replies
8
Views
439
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
747
  • Sticky
  • Article
Thanks so much for sharing this with us! I’ll definitely take a look, it seems like there are a lot of useful and interesting products. The idea...
    • Like
Replies
5
Views
2K

Similar threads

I don't think anyone on here is going to say it needs replacing, some may even argue that it's not even a c3.
    • Like
Replies
3
Views
480

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top