Hi can any one help me to clarify when exactly is supp bonding needed within a installation, i have read reg 415.2 in the bgb but it does not really clarify things, is they a specific reg i should be looking at?
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss Supp bonding in the Electrical Course Trainees Only area at ElectriciansForums.net
Hopefully this should already be in place as part of the standard protective measure for the location when it was originally installed, but if it is not present then it should be installed.I always got told in old properties that don't have RCD protection in areas with increased risk of electric shock, you supplementary bond metal work that can be simultaneously touched
Hopefully this should already be in place as part of the standard protective measure for the location when it was originally installed, but if it is not present then it should be installed.
If RCD protection, main bonding and ADS are present the the regulations permit the exclusion of supplementary bonding in a room containing a bath or shower.