When doing an I+T Today on a domestic property, i came accross a fault (C2) I thought might be of interest, its not the first time I have come accross it either.

The house was originally wired to the 16th in 2002.
It had a Night Store added in the bathroom in 2010, all legit. Completion cert part p etc.
This storage heater was wired from a new 16a rcbo in the board, the lighting, shower and downflow heater in the bathroom were not RCD protected but were supplementray bonded, as was all the pipework, The new nightstore was not.

This IMO is a C2 on an EICR as to allow the lighting and shower etc. to pass with a C3, all CPC's and conductive parts should be supplementary bonded.

I can see how the sparks failed to notice as all his new circuit was to the 17th but he inadvertently introduced a potential hazard.

Is it our responsibility as a sparks completing minor works/additions to check for situations like this and if necessary to install supp. bonding to our new circuit?

I think so but was just looking for others opinions.
 

Reply to Supplementary bonding + bathroom circuit additions. in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
285
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
786
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
804

Similar threads

  • Question
There could also be a completely unsuitable junction box embedded within the wall and tiled over or just cables in choc blocks in old accessory...
Replies
6
Views
981

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top