Is this an oil or gas boiler.
If oil it will need 'cross bonding'. If gas it will not.
4mm will be okay. Just put your clamps on the pipes and go from clamp to clamp with cut lengths. No need for it to be continuous across all clamps.
Why do you make a distinction between gas and oil when both services are likely to meet the definition of an extraneous-conductive part and be bonded accordingly?
Also, where is there a stated requirement in BS 7671:2008 to 'cross bond' a boiler regardless of fuel type?
I've given this some thought and it would seem that the normal scenario is that main protective bonding will be applied to the gas/oil supply and to the water supply in the usual manner.
The pipework at the boiler (flow/return, dhw) will be connected to a metallic manifold of some sort at the boiler but will not meet the definition of extraneous-conductive parts.
However, the boiler will have a cpc to it's casing/chasis which will in turn have continuity to the manifold.
The pipes are all now 'linked' in effect and there is no further hazard created by 'cross bonding' but the excercise would appear to be pointless and is certainly not a requirement.
Any thoughts anyone?