Who or what is/are eega?
Not this lot presumably:
East European Gas Analysis

Is this an oil or gas boiler.
If oil it will need 'cross bonding'. If gas it will not.

4mm will be okay. Just put your clamps on the pipes and go from clamp to clamp with cut lengths. No need for it to be continuous across all clamps.

Why do you make a distinction between gas and oil when both services are likely to meet the definition of an extraneous-conductive part and be bonded accordingly?

Also, where is there a stated requirement in BS 7671:2008 to 'cross bond' a boiler regardless of fuel type?

I've given this some thought and it would seem that the normal scenario is that main protective bonding will be applied to the gas/oil supply and to the water supply in the usual manner.
The pipework at the boiler (flow/return, dhw) will be connected to a metallic manifold of some sort at the boiler but will not meet the definition of extraneous-conductive parts.

However, the boiler will have a cpc to it's casing/chasis which will in turn have continuity to the manifold.
The pipes are all now 'linked' in effect and there is no further hazard created by 'cross bonding' but the excercise would appear to be pointless and is certainly not a requirement.

Any thoughts anyone?
 
My view on this subject is this.

1) We Main bond all extraneous conductive parts to the met. So if the gas and water are bonded at the entry job done. Now if the gas or water along the route of the installation are insulated(due to fitting etc ) at some point, theres no requirement to cross bond at this point.

Now if the boiler is in a special location, then we need to consider supplementary bonding. Now if the system complys with the section within 701.415.2 parts 1-3 then theres no requirement to supplementary bond. Note effectiveness of connection may be assessed using 415.2.2.. if all complys no supplementary bonding required. If the installation doesn't comply then supplementary bonding may be required including possible cross bonding.

If the boiler is outside the special location the only other issue may be that extraneous doesn't always mean earth potential, the boiler itself has the ability to provide mains potential. So if the boiler was non rcd and fed via a 3 amp fuse then theres a risk that a fault could develop, mains potential could be introduced.

I dont see the above as a problem in this case, i see no requirement to cross bond the boiler unless its in a special location and dose not meet the requirements.
 
Last edited:
Who or what is/are eega?
Not this lot presumably:
East European Gas Analysis

Is this an oil or gas boiler.
If oil it will need 'cross bonding'. If gas it will not.

4mm will be okay. Just put your clamps on the pipes and go from clamp to clamp with cut lengths. No need for it to be continuous across all clamps.

This is tosh I'm afraid....if you are going to post this sort of thing then you need to back it up with regulation numbers.
See post 18 for the correct information.
 
eaga are the guys paying, if they want cross bonding then do it regardless of where the boiler is, but cut lengths will do, ive been doing it for 4 years and never been pulled, also if the bath rad is a hard job then 'Bath Rad <0.05ohms' on your cert will do the trick as the cross bond is the same as bonding the bath rad
 
As it's unlikely to be a requirement of the BRB unless in a special location you can do it in wet string if you want to.

PMSL

The mythical art of cross bonding, seems it's making a come back, used to be able to make it look all curly and nice. No one ever could explain what it was for!
 
If you check the manufacturers instructions that come with most oil boilers carefully, you will find that they instruct to cross bond the pipes at the boiler.
Example:
http://www.worcester-bosch.co.uk/ca...nstructions-for-greenstar-danesmoor-18-25.pdf
Page 7 of the book, Page 9 of the pdf

My understanding is that gas boilers are designed to British Standards which require that the boiler design guarantees electrical continuity of pipes at the manifold, thus negating the need for any cross bonding. The standards oil boilers are designed to makes no such requirement.
 
Last edited by a moderator:

Reply to Supplementary Bonding on a boiler in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
348
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
888
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

H
  • Article
Boiler Programmer I have a wall mounted thermostat which is connected to a 26 volt supply from my Glowworm 24ci boiler. I would like to replace...
Replies
0
Views
102
homebrewer55
H
S
  • Article
Electrician Boiler Fault Boiler Fault I’m hoping someone can help with this boiler problem. Couple have just moved into a house that has a Grant...
Replies
0
Views
241
S

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top