hi all,

I know there are many questions on this topic but I'm unable to find my answer. Can I connect my 4mm supplementary bonding cable to the cpc in my shaver socket which then links directly back to the light (and via the cpc back to the CU)?

Sorry if it's a basic question, I am still training
 
Thanks Hightower. This is for my own bathroom, I am rewiring my house. My college tutor said that it's unlikely that all criteria to avoid supplementary bonding would be met so better to put it in.
 
Thanks Wilko. I am looking at 701.415.2 and under it I have written (curtesy of my tutor) "very hard to meet all conditions so better to put it in anyway, this will also cover future use/alterations" and "can only be omitted if maxresistance of extraneous conductive parts to the MET IS 1.66 ohms
 
Another possibly thick question, section (vi) all extraneous conductive parts are effectively connected to the protective equipotential bonding... Does this mean that the water pipes (e.g) are connected to the main incoming water pipe which is itself connected to the MET?
 
Hi - I think Tutor means less than 1.67k Ohms, from 50V / 30mA (assuming RCD). That's easily checked :)
The 3 conditions in 701.415.2 are easily complied with, I think. ADS tick, RCD tick, water and gas bonded to MET tick.
Maybe I am missing something?
Edit : yep, check bathroom for any extraneous conductive parts and bond if required. @Pete999 has a top video.
 
Last edited:
Thanks all. I'm glad at least my wiring is ok even if I didn't need to do it. On the plus side at least I don't have to do it for the other bathroom.
 
hi all,

I know there are many questions on this topic but I'm unable to find my answer. Can I connect my 4mm supplementary bonding cable to the cpc in my shaver socket which then links directly back to the light (and via the cpc back to the CU)?

Sorry if it's a basic question, I am still training
 
As others have said it's certainly not unlikely that all conditions for omitting supplementary bonding will be met where all bathroom circuits are RCD protected. That said, I personally prefer supplementary bonding as it does not require (an) electromechanical device(s) to be operating correctly. So you could install it in addition to (but certainly not instead of) RCD protecting all circuits of the location.
 
Sorry just noticed this thread is a few weeks old. Not sure why it appeared in the new topics section? Perhaps someone posted and then deleted their post.
 
Thanks anyway Risteard! I did put it in ready to be connected to the shaver socket but then it got taken out as the tiler forgot to run it up the wall to the shaver point! As others had said it wasn't really necessary I didn't put up a fight.
 

Reply to Supplementary bonding question in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
393
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
977
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
Surely one of the most important parts of supplementary bonding is to bond the radiator and hot tap/pipe to the cold one. Both the hot tap and...
Replies
32
Views
2K
  • Question
The chances of any problem without the RCD are minimal, including it extremely negligible......with the supplementary, on a kin to Hannibal Lector...
Replies
6
Views
767

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top