supplementary bonding | on ElectriciansForums
Discuss supplementary bonding in the Australia area at ElectriciansForums.net
T
timo
Just another quick one on a CU Swap. no bonding to bathroom, ktc etc. If the circuit is protected by 30Ma and the Water and Gas etc are bonded and also .4 disconnection is met then no requirement for bonding. Do you N/A the box on the check list?
Another requirement to omit supplementary bonding is a continuity reading of less than 1667 ohms between extraneous conductive parts and conductive parts....as long as all requirements are met them N/A in the tick box. I always note the continuity reading as well in the comments section.
Reply to supplementary bonding in the Australia area at ElectriciansForums.net
Surely one of the most important parts of supplementary bonding is to bond the radiator and hot tap/pipe to the cold one. Both the hot tap and...
Generally speaking local earthing will rarely be below a couple of ohms, so in parallel with a TN-S sub-ohm value will make little difference...