is ok to take a 10mm earth out of a cooker point to a water pipe?? if not what would the code be?
is the consumer unit etc up to scratch with 17th edition? rcd's etc? just thinking if so then supplementary bonding is not required. (if the cable you are talking about is just acting as a supplementary bonding i.e bonding pipes to taps) if its the equipotential bonding (main bonding to incoming water pipe) then this will not be adequate and you will need to run a new 10mm earth direct to the consumer unit
Reply to supplementary bonding in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Any metalwork connected to the MET could rise in voltage compared to true earth under an open supply neutral fault (on TN-C-S), and that would...
Surely one of the most important parts of supplementary bonding is to bond the radiator and hot tap/pipe to the cold one. Both the hot tap and...