Met someone the other day, he told me he was a lecturer teaching electrical installation at the local collage, he said that if you have main water and gas bonded you don't need any supplementary bonding regardless of whether you have RCD protection or not. I didn't want to argue with him too much as he is a teacher but I was pretty sure that it only applies if all circuits are RCD protected? Is this some new rule I've missed?
 
Last edited:
Jesus Christ, where do I start?

You are confusing equipotential bonding with supplementary bonding...that's bad enough. But the R1 + R2 for a RFC comment just beggars belief!

Give up before you kill someone!
Wind your neck in, I was stating the value to be remembered for certain applications, you might remember it now...
 
rubbish! if the cpc of a circuit in a bathroom has a resistance of >0.05 ohms, how would you achieve 0.05 between ext. metalwork and the cpc?
 
supp. bonding would only get you 0.05 between ext. pipes, unless you added supp. bonding from fittings to pipes. look good, a few yards of 4mm or 6mm gn/y cable on the tiles.
 
I think that a few people actually need to read the regs on here before discounting the need for RCD protection without supplementary bonding.... Figures have absolutely nothing to do with it.
Tell you what, as I'm in a good mood tonight... 701.415.2
 
This thread just gon ---- up, all over the place. 1667 ohms stable not stable, 0.05 ohms and rings, etc. I just got dizzy with no beer. the only number you need to know with sup bond is 23 kohm, that's about it.
 
Amazing amount of mis-information posted on this thread.
The effectiveness of the connection of ECP's in a bathroom/shower room to the MET/main bonding may be determined by the application of 415.2.2.
Which effectively means where a 30ma RCD is in place a continuity reading of <1667 ohms between CP's and ECP's within the location = satisfactory supplementary bonding.
For a 6a type B mcb a continuity reading of <1.66 ohms = satisfactory supplementary bonding.
 
Last edited by a moderator:
This thread just gon ---- up, all over the place. 1667 ohms stable not stable, 0.05 ohms and rings, etc. I just got dizzy with no beer. the only number you need to know with sup bond is 23 kohm, that's about it.

Yeah your right, thats taking the human body resistance into account at 1000ohms and 230v supply.
And thats the measurement from the bathroom zones to the MET.
I was taught the 0.05 ohm measurement between PE terminals and extraneous conductive parts in the bathroom.
I will try and find that in writing (I hope I can for my sake, its like a bear pit around here!!)
and post it.
In my inspection and test assessments they made a big deal of this figure not being exceeded.
 
Yeah your right, thats taking the human body resistance into account at 1000ohms and 230v supply.
And thats the measurement from the bathroom zones to the MET.
I was taught the 0.05 ohm measurement between PE terminals and extraneous conductive parts in the bathroom.
I will try and find that in writing (I hope I can for my sake, its like a bear pit around here!!)
and post it.
In my inspection and test assessments they made a big deal of this figure not being exceeded.

I think your figure of 0.05 ohms came from guidence( and only guidence), that when testing continuity of your protective bonding conductors, even though you just put a tick in box on your certificate it "SHOULD" be under 0.05 ohms, which is derived from formula too, can not think exactly from my head at this min, and us I said it is only guidence, dont remember seeing this figure anywhere in the regs book.
 

Reply to the thread, titled "Supplementary bonding?" which is posted in UK Electrical Forum on Electricians Forums.

Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Daily, weekly or monthly email

Back
Top