Supplemntary Bonding (lack Of) What Code? | on ElectriciansForums

Discuss Supplemntary Bonding (lack Of) What Code? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Joined
Feb 9, 2011
Messages
1,251
Reaction score
357
Hi all,
Been a while but I'm back with a question!
I have just started Testing using the New EICR format, Generally not to bad but I have a few gripes, one of them being supplementary bonding.
According to the 'Best Practise guide' Lack of a 30ma RCD or Supplementary bonding in a bathroom is now a code 2 meaning fail.

However if the installation was installed to the 14th edition, (pre supplementary bonding), how can this still be a c2?

NICEIC helpline were next to useless and told me that you have to test it to the regulations, however I have always been told you cannot apply regulkations retrospectively?

What would you put?
 
Doesnt the 0.05 Ohm between points come in here, if that tests out ok then bonding deemed not req,or not visible point me out if im barking up the wrong tree here
 
Doesnt the 0.05 Ohm between points come in here, if that tests out ok then bonding deemed not req,or not visible point me out if im barking up the wrong tree here

Kind of on the right track, yes.

Essentially there are 3 conditions that must be met in order for supplementary bonding to be omitted.

701.415.2, (iv), (v) & (vi).
 
I understand the conditions which need to be met to omit it, however if the installation dates to 14th edition territory, can it now be failed as it complied when installed?

I was always told regulations cannot be applied retrospectively?
 
When you carry out an eicr, you are not applying the regulations. You are reporting on the condition of the installation against current regulations.
 
For an EICR it is primarily a report to assess if the installation is safe for continued use without risk of shock, burns etc.
If an installation complied with an earlier edition of the regulations it does not necessarily mean it is not safe, however it also does not force it to be safe.
The current interpretation is that the risk of electric shock is higher in wet areas and this risk can be mitigated by the use of RCDs, ADS and main bonding or employing supplementary bonding. If there is no supplementary bonding or an RCD then there is an increased risk of electric shock in the case of a fault. So C2 potentially dangerous sounds applicable in this case.
 
If a installation was done after 2008 ie 17th edition rcd protection 10mm to water and gas 16mm main earth then no bonding is required am I right prior to 2008 bonding supplementary bonding is required and any installations that don't comply you code and report appropriately
 
Is it correct to say this install is satisfactory and recorded as so (as at time of install it complied with current regs) but you add requires improvement. I understand it is not a legal requirement to upgrade though??? Anyone can confirm this is correct please.Thank you
 
Times change.
What was considered safe in the 60s and 70s, is not neccessarily considered safe today.
When the 14th was current, baths were allowed in kitchens.
Yes it may be that at the time of construction, the installation complied with the Regulations.
However, I doubt very much that the installation has remained unchanged since it was constructed.
I also doubt that the fixtures and fittings in the building have remained unchanged.
Is there for instance a radiator in the bathroom, I doubt it was there at the time the installation was constructed.
 
Last edited by a moderator:

Reply to Supplemntary Bonding (lack Of) What Code? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
264
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
756
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
740

Similar threads

I usually put something like this To assess compliance with BS7671 for continued safe operation (5 year periodical inspection)
Replies
8
Views
438
In the 80's I was taught that with PME earthing arrangements we used 16mm for the main earthing conductor, some went a bit crazy and were bonding...
Replies
11
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top