In our place we have several machines that are fed from 63A sockets. The supply cable to the machines is CY and currently
6mm has been used which is no good for 63A
But the 63A sockets are fed by a 32A breaker.
Is it ok to use the 6mm as the socket is fed by a lower rated breaker?
I'm a bit unsure on this one, on one hand if the supply is ok and fed at 32A it should be ok BUT what if someone plugs the machine into a socket that is fed at 63A (if we have any - need to check) this would be well outside the regs - from memory i think we would need 16A cable for 63A
If this is in the regs can you point me in the right direction.
Cheers
In our place we have several machines that are fed from 63A sockets. The supply cable to the machines is CY and currently
6mm has been used which is no good for 63A
But the 63A sockets are fed by a 32A breaker.
Is it ok to use the 6mm as the socket is fed by a lower rated breaker?
I'm a bit unsure on this one, on one hand if the supply is ok and fed at 32A it should be ok BUT what if someone plugs the machine into a socket that is fed at 63A (if we have any - need to check) this would be well outside the regs - from memory i think we would need 16A cable for 63A
If this is in the regs can you point me in the right direction.
Cheers