Hi ,I have a wood cabin outside 70mtrs from house incoming supply, I was thinking of using a 35mm 2core pvc/swa, as I think a TT system would be appropriate for the cabin, owing to the distance away from house load would be allowing for diversity would be 51amps, seems a lot but it will be a live in dwelling with all requirements for cooking heating etc,am i correct with supply size Thanks ron
 
Whilst cable size has been worked out to 25 or 35 due thought needs to be given to the terminal sizes and termination practicalities.

You can buy pin lugs to reduce 35mm to 25mm, since the 35mm size is only required for VD an not load, there is no issue in this solution.

Don't see why at that size you can't use the house's earthing system. Utilizing the armor of the SWA as a CPC. Unless you have extraneous services entering the outbuilding.

A switch fuse would be more ideal to provide protection for this cable, purely to meet discrimination with MCB's that I presume are going to be installed in the outbuilding.
 
Last edited by a moderator:

Reply to supply cable sizing in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
288
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
790
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
811

Similar threads

  • Question
If your using 35mm or 50mm use 2 core SWA and use the armour as the earth, it'll cut down on price. I know people will comment on this but the...
Replies
10
Views
1K
  • Question
If it is TT then you can use the armour of any of them as CPC but will almost certainly need an up-front delay RCD at the sub-main feed point to...
Replies
5
Views
939

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top