I’m going to be pedantic here....

Cable goes through ceiling void, then underground.

Low ceiling or very high ground outside??
Is there a vertical part of that route that hasn’t been measured?


What my esteemed colleagues are getting at, is that this job is notifiable to local council under Part P building regs. Unless you live in Scotland, where we can get away with it.
 
Multicore 90°C Armoured Thermosetting Insulated Cables
Tables Apply to: H6942XL, H6943XL, H6944XL, H6945XL, Tuff Sheath,

Voltage: 230V

Load: 14.72kW / 64A

Length: 45m

Method of Installation: Direct in ground or in ducting in ground

Cable Size: 16mm²

Of course, only suitable if the equipment it is being connected to is rated for 90 dec C.
 
Of course, only suitable if the equipment it is being connected to the devil
She-Devil-with-crazy-laugh_1537.jpg


is rated for 90 dec C.
LOL.
 
Sorry all but why RCD at the local db? why not RCD at the CU and MCBs at local db. Thinking cable protection, is this so an RCD trip is local rather than remote.
 
I’m going to be pedantic here....

Cable goes through ceiling void, then underground.

Low ceiling or very high ground outside??
Is there a vertical part of that route that hasn’t been measured?


What my esteemed colleagues are getting at, is that this job is notifiable to local council under Part P building regs. Unless you live in Scotland, where we can get away with it.

When did this become a domestic installation? The OP hasn't mentioned what type of installation it is, but it does sound a bit like a school.
 
Sorry all but why RCD at the local db? why not RCD at the CU and MCBs at local db. Thinking cable protection, is this so an RCD trip is local rather than remote.

Because you end up with the whole portacabin on one rcd, so the whole thing goes off if it trips.
There is unlikely to be any need for the submain to be RCD protected.
 
Multicore 90°C Armoured Thermosetting Insulated Cables
Tables Apply to: H6942XL, H6943XL, H6944XL, H6945XL, Tuff Sheath,

Voltage: 230V

Load: 14.72kW / 64A

Length: 45m

Method of Installation: Direct in ground or in ducting in ground

Cable Size: 16mm²

In the cable calculation, the cable will need to be derated to a maximum operating temperature of 70 degrees celsius as per BS7671 regulation 512.1.2
 
In the cable calculation, the cable will need to be derated to a maximum operating temperature of 70 degrees celsius as per BS7671 regulation 512.1.2

See post #20 above.
 

Reply to Supply cable to portacabin in the The Welcome Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
300
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
812
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
865

Similar threads

I might have got lost here, but the rotary iso is rated at 63A so 25mm armoured still wouldn't make the install satisfactory. Assuming everything...
Replies
7
Views
487
  • Question
That was my saying not long ago about TNS to PME system. I would be nice you can ring up the DNO, will the systems being up graded, there is a...
Replies
9
Views
2K

Search Electricans Forums by Tags

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top