43a KILN in a house ?? I recon that would be a NONO on the supply front and I wouldnt want to live in the same block as drawing 43a While Im having a shower may result in me getting a cold shower
as for the council Im sure they would wonder why you wanted a 43a Kiln in the house if not for buisness and doubt your tennancy would allow for buisness to run from the house

Council have approved it (it's a flat as above...), this flat is actually going to be used as a studio, it's not going to effect other flats it's the max rating for a start. and they have there own supply like ive said above....
 
You have stated that a 60A fuse is protecting a 57A (tops) cable. The purpose of the protective device is to protect the Cable. You have already stated that this will not happen.
 
no way is any kiln getting connected without a serious assessment of the properties load demand and the impact on the cables / switchgear upstream.
i would not take the word of any council spark , do the above yourself to be certain.
is it your name on the design section of the EIC ?
 
why not take the word of council Sparks who has actualy seen the cable and condition Looks like he is willing to take the word of a bunch of guys on line who havent seen the things he is babbling about and have been drip fed what he is proposing
 
The ENTIRE block is probably only fed via 3x 100/200A BS88 fuses.

Your neighbours will love you when that pops and no one has any power.

Surprised the council are letting you make alterations to the wiring, the council I work for forbid that.
 

Reply to Supply cable to small or not? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Hi everyone, If you are looking for reliable EV chargers, check out our top-rated selection at E2GO! ⚡ Please note that all EV Chargers and...
Replies
0
Views
170
  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
1K
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K

Similar threads

I might have got lost here, but the rotary iso is rated at 63A so 25mm armoured still wouldn't make the install satisfactory. Assuming everything...
Replies
7
Views
634
  • Question
This is an interesting issue. I agree with you however I took this to task with a scam inspector some years ago and we agreed to disagree that...
2
Replies
29
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top